Main elements library of the user interface

Name: wlb_Main
Founded: september 2007
Version: 1.1.0
State: Open (GPL)
Author: Roman Savochenko, Maxim Lysenko (2011-2012)
Description: Provides the library of the main elements of the user interface.
Address: DB is in the file: SQLite.vcaBase.wlb_Main (vcabase.db.gz)


Contents

About the library

The library is created to provide mnemonic elements of the user interface. The library is built on the basis primitives of widgets and JavaLikeCalc module, allowing to create calculations on the Java-like language.


It is possible to connect the library of mnemonic elements of user interface to the project of the OpenSCADA station by downloading the attached file of the database, placing it in in the database directory of the station's project and creating the database object for the DB module "SQLite", indicating the database file in the configuration.


The library contains about two dozen graphic elements, often sought when forming the user interface of process control. Names and text options are available in three languages: English, Russian and Ukrainian.

1. Analog show (anShow)

The element, shown in Fig. 1, is used to display the current value of the analog parameter and modes of regulator, if the parameter is regulator. Also, this element generates alarms on the relevant parameter settings.


"Analog show" widget in the development mode (2 Кб) "Analog show" widget in the runtime mode (2 Кб)
Fig.1. "Analog show" widget in the development and runtime modes (left to right).

Using - Development

This widget can be used by developer to create mimics to display the values of analog parameters and PID regulators. To use it you need to add this widget to mimic and link to the data source parameter.

Using - Runtime

At runtime mode, you can obtain the passport for parameter by clicking the right mouse button on the body of the widget. The passport will present all the properties of the parameter. Pressing the left mouse button in the body of the widget the control panel will appear parameter, and the selection of this widget will be displayed with blinking frame.

Linking attributes

IDParameterData typeConfigConfig templateDescription
pErr Error String Input link Parametr|err

Code and text of the error of the parameter. It is used to generate alarm. The following error codes are processed:

  • 1,2 - failure, parameter is not valid;
  • 3 - above the admissible limit;
  • 4 - below the admissible limit;
  • 5 - above normal;
  • 4 - below normal.
pModeA Regulator mode (auto) Boolean Input link Parametr|auto When adjusted on the left of the value the large letter "A" is displayed.
pModeC Regulator mode (cascade) Boolean Input link Parametr|casc When adjusted on the left of the value the large letter "C" is displayed.
pName Parameter's name String Input link Parametr|NAME Short name of the parameter displayed over the value.
pPrec Precision Integer Input link Parametr|prec Number of decimal places for value.
pVal Parameter's value Real Input link Parametr|var Direct parameter's value.
redEVAL Red parameter name in case of failure Boolean Constant
By default, the color of the parameter's name for the "failure" state(EVAL value) is gray. But some critical for the process parameters must have the "failure" state displayed with the red parameter's name.
spName Speech name String Constant
The name of the parameter for speech synthesis during the formation of alarm messages taking into account accents of words, pauses, etc.

2. Analog show 1 (anShow1)

The element, shown in Fig. 2, is used to display the current value of the analog parameter with a one-character prefix of the type of measured value.


"Analog show 1" widget in the development mode (1 Кб) "Analog show 1" widget in the runtime mode (1 Кб)
Fig.2. "Analog show 1" widget in the development and runtime modes (left to right).

Using - Development

This widget can be used by developer to create mimics to display the values of analog parameters. o use it you need to add this widget to mimic and link to the data source parameter.

Linking attributes

IDParameterData typeConfigConfig templateDescription
pName Parameter's name String Constant Parametr|NAME One-character prefix of the type of measured value.
pVal Parameter's value Real Input link Parametr|var Direct parameter's value.
pPrec Precision Integer Input link Parametr|prec Number of decimal places for value.

3. Element cadr (ElCadr)

The element, shown in Fig. 3, is essentially a universal control panel of various devices:

"Element cadr" widget in the development mode. (16 Кб)
Fig.3. "Element cadr" widget in the development mode.

Using - Development

This widget is not intended for special placement and configuration of the user, as laid down in the "Signal groups" template and if the new project is created from this template, the call of the widget is done automatically, with its display in the control panel area when you select a widget of the parameter, which provides the parameter's control, for example, previously considered "anShow ".

Using - Runtime

Fig. 4 shows various examples of this element in the runtime mode.


"Element cadr" widget in the runtime mode. (38 Кб)
Fig.4. "Element cadr" widget in the runtime mode.

Modes:


Every action on this panel (change of PID set point, state of the discrete parameter ...) is recorded in the actions log by the generation of appropriate messages.


For any displayed or controlled parameter the passport can be obtained in runtime mode by clicking the right mouse button on the contour field. The passport will present to all the properties of the parameter.

Linking attributes

IDParameterData typeConfigConfig templateDescription
prmId Parameter:identifier String Input link Parametr|SHIFR Parameter's identifier is used to place the record the operator's actions to the report.
prmShifr Parameter:code String Input link Parametr|NAME Short name of the parameter, code. It is placed below the frame.
prmDescr Parameter:description String Input link Parametr|DESCR Description of the parameter is used to place the record the operator's actions to the report.
prmColor Parameter:border color String Input link Parametr|color Sets the border color of the contour.
Parameters of Analog Device
prmDemention Parameter:dimension variable String Input link Parametr|ed
prmPrec Precision Integer Input link Parametr|prec Number of decimal places in parameter, step change for the manual input of values, as well as set point and out of the PID regulator.
prmVar Parameter:variable Real Full link Parametr|var Directly to the analog value of the parameter.
max Parameter:maximum Real Input link Parametr|max Upper limit value of the parameter.
min Parameter:minimum Real Input link Parametr|min Minimum limit values of the parameter.
prmAMax Upper alarm border Real Input link Parametr|aMax
prmAMin Lower alarm border Real Input link Parametr|aMin
prmWMax Upper warning border Real Input link Parametr|wMax
prmWMin Lower warning border Real Input link Parametr|wMin
Manual Analog Input
prmVarIn Parameter:variable input Real Full link Parametr|varIn Output for manual input of an analog value of the parameter. The presence of this parameter is an indication that the parameter - is determined as "Manual analog input.
PID regulator
prmAnalog Parameter:analog regulator Boolean Input link Parametr|analog Sign of the analog regulator, in case of the absence of this parameter the regulator is an analog one.
prmAuto Parameter:automate Boolean Full link Parametr|auto Mode of the regulator, "Automatic".
prmCasc Parameter:Cascade Boolean Full link Parametr|casc Mode of the regulator, "Cascade".
prmSp Parameter:set point Real Full link Parametr|sp PID regulator's set point, it can be set by the user.
prmImpQdwnTm Parameter:imp. out down Boolean Input link Parametr|impQdwn Output "Down" for impulse regulator.
prmImpQupTm Parameter:imp. out up Boolean Input link Parametr|impQup Output "Up" for impulse regulator.
prmOut Parameter:output Real Full link Parametr|out Analog PID regulator output for display and manual input of the output value of PID in manual mode.
prmManIn Parameter:manual input Real Full link Parametr|manIn Manual input of the new output value of PID regulator in manual mode.
Parameters of discrete devices
prmCom Parameter: Command - "Open" Boolean Full link Parametr|com
prmClose Parameter: Command - "Close" Boolean Full link Parametr|close
prmStop Parameter: Command - "Stop" Boolean Full link Parametr|stop
prmOpenSt Parameter: State - "Opened" Boolean Input link Parametr|st_open
prmCloseSt Parameter: State - "Closed" Boolean Input link Parametr|st_close
digComs Parameter:digital commands String Input link Parametr|digComs Names and colors of buttons of commands in the format: {On}[-color]:{Off}[-color][:{Stop}[-color]]. Default colors are: green, red and yellow.
digStts Parameter:digital states String Input link Parametr|digStts Names and colors of labels of states in the format: {On}[-color]:{Off}[-color]. Default colors are: green and red.

4. Contours group (grpCadr)

Element, shown in Fig. 5, provides for simultaneous monitoring and control of several contours up to eight, includes both instances of the widget "Element cadr for each contour, and a widget "Diagram" to monitor the trends of the contours and viewing history .


"Contours group" widget in the development mode. (30 Кб)
Fig.5. "Contours group" widget in the development mode.

Using - Development

This widget is designed to perform the role of page-template, and should therefore be placed directly in the project's tree. The project-template "signal groups" for each signal object that widget-frame is included in the role of a template that allows you to create on its basis a set of pages of groups of contours. For each widget-frame, it can be connected up to eight parameters by setting the links. Contours for which there is no set links will be hidden at runtime.

Using - Runtime

In runtime mode, the contours and trends, for which links have been set, are displayed. Control of the parameters by contours, respectively described in detail in the section of the "Element cadr (ElCadr)" widget. In addition to this you can control the trends display properties, which requires the left mouse button to click in the trend's area and by means of appeared trend's control panel to make the necessary actions.


Fig. 6 is an example of this element in the runtime mode.


"Contours group" widget in the runtime mode. (36 Кб)
Fig.6. "Contours group" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
grpName Group name String Constant
Group's name
Element {n} from 1 to 8.
el{n} The list of linking parameters corresponds to the list of the "Element cadr (ElCadr)" widget

5. Views page's element (ElViewCadr)

Element, shown in Fig. 7, serves as the basis for overview frames panel and is not usually used independently. Element reflects the text information about a parameter in the form of the name and value, and a graph (trend) of the parameter for a small (adjustable) period of time to observe the current trend of the parameter with auto-scaling on the value's scale.


"Views page's element" widget in the development mode. (2 Кб)
Fig.7. "Views page's element" widget in the development mode.

Using - Development

Though this widget is not intended for independent use, in isolation from frames panel, it can be used, for example, by placing it to the mimic and linking with the data source parameter.

Using - Runtime

At runtime mode, you can obtain the passport for parameter by clicking the right mouse button on the body of the widget. The passport will present all the properties of the parameter. Pressing the left mouse button in the body of the widget the control panel will appear parameter, and the selection of this widget will be displayed with blinking frame.


Fig. 8 shows various examples of this element in the runtime mode.


"Views page's element" widget in the runtime mode. (5 Кб)
Fig.8. "Views page's element" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
name Name String Input link Parametr|NAME Parameter name, code, for display in the name's field.
addr Address Address Input link Parametr|var Address to the attribute of the parameter's values for trend's building.
var Variable Real Input link Parametr|var Direct value of the parameter to display in value's field.

6. Overview frames panel (ViewCadr)

Element, shown in Fig. 9, serves to show the current trends for the parameters of the signal object up to 24 pieces, supports scaling elements depending on their number. Consists of widgets "views page's element (ElViewCadr)".


"Overview frames panel" widget in the development mode (12 Кб)
Fig.9. "Overview frames panel" widget in the development mode.

Using - Development

This widget is designed to perform the role of template-page, and should therefore be placed directly in the project's tree. The project-template "signal groups" for each signal object that widget-frame is included in the role of a template that allows you to create on its basis a set of pages of groups of overview frames panel. To each widget-frame can be connected to the 24-parameter by setting the links. Trends for which there is no set links will be hidden at runtime, and when it is necessary the expansion and scaling of linked ones will be done to fill the area of the widget.

Using - Runtime

In the runtime mode the trends' contours are displayed, for which links have been set. Control of the parameters from contours, respectively described in details in the section "views page's element (ElViewCadr)" widget.


Fig. 10 shows an example of this element in the runtime mode.


"Overview frames panel" widget in the runtime mode. (12 Кб)
Fig.10. "Overview frames panel" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
name Name String Constant
Frame's name
Element {r}_{c}, where {r} - rows from 1 to 4 and {c} - columns from 1 to 6.
el{r}_{c} The list of linked parameters corresponds to the list of ones of the "Views page's element (ElViewCadr)" widget

7. Graphics group element (ElViewGraph)

Element, shown in Fig. 11, is provided to create graphics groups. Element contains information about a parameter, the regulator's mode if the parameter is such, the units of analog parameter, as well as the color corresponding to the parameter's trend.


"Graphics group element" widget in the development mode. (2 Кб)
Fig.11. "Graphics group element" widget in the development mode.

Using - Development

Though this widget is not intended for independent use, in isolation from graphics groups, it can be used, for example, by placing it to the mimic and linking with the data source parameter.

Using - Runtime

At runtime, except the available visual data, provided by a number of control elements:


Fig. 12 shows various examples of this element in the runtime mode.


"Graphics group element" widget in the runtime mode. (6 Кб)
Fig.12. "Graphics group element" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
name Name String Input link Parametr|NAME Parameter name, code, for display in the name's field.
addr Address Address Input link Parametr|var Address to the attribute of the parameter's values for trend's building.
color Trends color String Constant
Parameters of Analog Device
ed Dimension String Input link Parametr|ed
prec
Precision
Integer Input link Parametr|prec Number of decimal places in parameter.
max Maximum Real Input link Parametr|max Upper limit value of the parameter.
min Minimum Real Input link Parametr|min Minimum limit values of the parameter.
aMax Upper alarm border Real Input link Parametr|aMax
aMin Lower alarm border Real Input link Parametr|aMin
wMax Upper warning border Real Input link Parametr|wMax
wMin Lower warning border Real Input link Parametr|wMin
pModeA "Automate" regulator's mode Boolean Input link Parametr|auto Mode of the regulator, "Automatic".
pModeC "Cascade" regulator's mode Boolean Input link Parametr|casc Mode of the regulator, "Cascade".
Parameters of discrete devices
digComs Digital commands String Input link Parametr|digComs Names and colors of buttons of commands in the format: {On}[-color]:{Off}[-color][:{Stop}[-color]]. Default colors are: green, red and yellow.
digStts Digital states String Input link Parametr|digStts Names and colors of labels of states in the format: {On}[-color]:{Off}[-color]. Default colors are: green and red.
digRevers Revers Boolean Constant
Discrete signal reverse.

8. Graphics group (grpGraph)

Element, shown in Fig. 13, is provided for simultaneous observation of a trend and control the parameters of the signal object, includes both instances of the widget "Graphics group element (ElViewGraph) " for each parameter and widget "Diagram" to monitor the parameters' trends and browsing history, and also scroll bar for fast navigation on allowed history of selected parameters for show.


"Graphics group" widget in the development mode. (16 Кб)
Fig.13. "Graphics group" widget in the development mode.

Using - Development

This widget is designed to perform the role of page-template, and should therefore be placed directly in the project's tree. The project-template "signal groups" for each signal object that widget-frame is included in the role of a template that allows you to create on its basis a set of pages of graphics group. For each widget-frame, it can be connected up to eight parameters by setting the links. Trends for which there is no set links will be hidden at runtime or allowed for user's selection at case allowing parameters for selection list in attribute "Allow for select parameters" (list format described into parameters selection dialog).

Using - Runtime

In runtime mode, the trends, for which links have been set, are displayed. Control of the parameters from the text elements of the trends, respectively described in detail in the section of the "Graphics group element (ElViewGraph)" widget. In addition to this you can control the trends display properties, which requires the left mouse button to click in the trend's area and by means of appeared trend's control panel to make the necessary actions.


Fig. 14 shows an example of this element in the runtime mode.


"Graphics group" widget in the runtime mode. (25 Кб)
Fig.14. "Graphics group" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
grpName Group name String Constant
Group name
Element {n} from 1 to 8.
el{n} The list of linking parameters corresponds to the list of the "Graphics group element (ElViewGraph)" widget

9. Result graphic's element (ResultGraphEl)

Element, shown in Fig. 15, is provided to create result graphics. Element allows you to display trends on the five parameters for a specified period of time till the current time.


"Result graphic's element" widget in the development mode. (4 Кб)
Fig.15. "Result graphic's element" widget in the development mode.

Using - Development

Though this widget is not intended for independent use, in isolation from result graphics, it can be used, for example, by placing it to the mimic and linking with the data source parameter.


Fig. 16 shows an example of this element in the runtime mode.


"Result graphic's element" widget in the runtime mode. (4 Кб)
Fig.16. "Result graphic's element" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
title Title String Constant
It is displayed above the graph. If the title is missing the trend's field will expand up.
Trend {n} from 1 to 5.
p{n}_addr Parameter{n}:address Address Input link Parametr_{n}|var Address to the value's attribute for {n} trend's building.
p{n}_clr Parameter{n}:color Color Constant Parametr_{n}
p{n}_max Parameter{n}:maximum Real Input link Parametr_{n}|max Upper limit of the trend.
p{n}_min Parameter{n}:minimum Real Input link Parametr_{n}|min Lower limit of the trend.
p{n}_name Parameter{n}:name String Input link Parametr_{n}|NAME The short name of the parameter to display in the field on the left.

10. Result graphics (ResultGraph)

Element, shown in Fig. 17, is used to display the trends of the parameters of the whole visualization project.


"Result graphics" widget in the development mode. (23 Кб)
Fig.17. "Result graphics" widget in the development mode.

Using - Development

This widget is designed to perform the role of page-template, and should therefore be placed directly in the project's tree. In the project-template "signal groups" on the root page level there is special virtual page "Result graphics" with the result graphics template, that allows you to create on its basis a set of pages of result graphics. To each widget-frame can be connected to the 16*5 parameters by setting the links. Trends, for which there is no set links, will be hidden at runtime, and when it is necessary the expansion and scaling of linked ones will be done to fill the area of the widget.

Using - Runtime

In runtime the contours of the trends, for which the links are set, are displayed.


Fig. 18 shows an example of this element in the runtime mode.


"Result graphics" widget in the runtime mode. (27 Кб)
Fig.18. "Result graphics" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
grpName Group name String Constant
Group name
Element {n} from 1 to 16.
el{n} The list of linking parameters corresponds to the list of the "Result graphic's element (ResultGraphEl)" widget.

11. Regulator's control panel (cntrRegul)

Element, shown in Fig. 19, is used for adjustment of PID regulator, includes information about the parameter-regulator, fields of the regulator's settings, and the "Diagram" widget to monitor the trends of the regulator and browsing history.


"Regulator's control panel" widget in the development mode. (35 Кб)
Fig.19. "Regulator's control panel" widget in the development mode.

Using - Development

This widget can be used as a panel, called from the control of panel of the parameters "ElCadr", as well as a template-page. Widget should be placed directly in the project's tree, namely to the panels' container, where the dynamic linking will be implemented to the regulator's parameter. To create the static list of the regulator's settings contours, with the possibility of paging in it, you must place them in a container of regulator's contours "greg" of each signal object and statically link them with the corresponding parameter, and to ensure equality of the panel's ID and linked parameter.

Using - Runtime

In the runtime mode the following fields are displayed:


Users have the ability to change the PID regulator's coefficients: mode, set point, out and immediately to see the reaction on the diagram. In addition, the user can learn the history of the regulator, which requires the left mouse button click in the graph area and by means of appeared trend's control panel to make the necessary navigation actions. To return the control panel of the parameter the left mouse button to click in an empty area of the frame is required.


Fig. 20 shows an example of this element in the runtime mode.


"Regulator's control panel" widget in the runtime mode. (49 Кб)
Fig.20. "Regulator's control panel" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
SHIFR Code String Input link Parameter|SHIFR
NAME Name String Input link Parameter|NAME
DESCR Description String Input link Parameter|DESCR
max Scale maximum Real Input link Parameter|max
min Scale minimum Real Input link Parameter|min
ed Units String Input link Parameter|ed
prec Precision Integer Input link Parametr|prec Number of decimal places in value and set point of the PID.
var Variable String Input link Parameter|var
var_addr Variable address Address Input link Parameter|var Address for the trend's building of the value.
PID - regulator
auto_addr Mode Address Input link Parameter|auto Address for the "Automate" mode trend's building.
sp Set point Real Input link Parameter|sp
sp_addr Set point address Address Input link Parameter|sp Address for the trend's building of the set point.
out Out Real Input link Parameter|out
out_addr Out address Address Input link Parameter|out Address for the trend's building of the analog output.
Hdwn Bottom output border Real Full link Parameter|Hdwn Restricting the values of the analog output on the bottom.
Hup Top output border Real Full link Parameter|Hup Restricting the values of the analog output on the top.
Kp Gain coefficient Real Full link Parameter|Kp
Ki Coeff. of integration Real Full link Parameter|Ki
Ti Integration time Real Full link Parameter|Ti
Kd Coeff. of differential Real Full link Parameter|Kd
Td Differentiation time Real Full link Parameter|Td
Tzd Differential part lag time Real Full link Parameter|Tzd
Zi Insensitivity area Real Full link Parameter|Zi
K1 Input 1 coefficient Real Full link Parameter|K1
K2 Input 2 coefficient Real Full link Parameter|K2
K3 Input 3 coefficient Real Full link Parameter|K3
K4 Input 4 coefficient Real Full link Parameter|K4
Pulse PID - regulator
impQup_addr Address of impulse output up Address Input link Parameter|impQup
Address for the trend's building of the pulse output "Up".
impQdwn_addr Address of impulse output down Address Input link Parameter|impQdwn Address for the trend's building of the pulse output "Down".
KImpRfact Rate factor Real Full link Parameter|KImpRfact The asymmetry in the generation of pulse-width up and down.
TImpMin Minimal impulse time Integer Full link Parameter|TImpMin There will be generated impulses, starting with the specified width.
TImpPer Impulses period Integer Full link Parameter|TImpPer Frequency of repetition of pulse generation.

12. Root page (SO) (RootPgSo)

The "Root page" element, shown in Fig. 21, serves as the basis for creating the process control user interfaces, grounded on the signal object. The root page contains four areas:


Under control panels container placed button for demo mode start — mode on which performed periodic switching for representative frames, changing regime and other operations by scenario.


"Root page (SO)" widget in the development mode. (43 Кб)
Fig.21. "Root page (SO)" widget in the development mode.

Using - Development

This widget can be used only in the root page mode that should be placed in the project's tree as an element "/*/so". In addition, around the main page should be made following tree hierarchy:


At demo mode present you should into attribute "Procedure play demo" describe demo procedure on internal language OpenSCADA DAQ.JavaLikeCalc. For example bellow led demo procedure of "Dynamic model AGLKS":

stepCur++; stepTm = 20;
//>> Open main mnemo
if(stepCur == 0)
{
	this.pg_1.pg_mn.pg_1.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Main mnemo open.");
}
//>> Open main graphics
else if(stepCur == 1)
{
	this.pg_1.pg_ggraph.pg_1.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Main graphics open.");
}
//>> Setpoint set more for PC KRD1
else if(stepCur == 2)
{
	SYS.DAQ.BlockCalc.Anast1to2node_cntr.PC_ΚΠΔ1.sp.set(6);
	this.attrSet("tipStatus","The regulator PC_KRD1 setpoint increase.");
}
//>> Open contours group
else if(stepCur == 3)
{
	this.pg_1.pg_gcadr.pg_1.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Contours group open.");
}
//>> Open overview cadr
else if(stepCur == 4)
{
	this.pg_1.pg_gview.pg_1.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Overview frame open.");
}
//>> Open document
else if(stepCur == 5)
{
	this.pg_1.pg_doc.pg_1.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Document open.");
}
//>> Open result graphics
else if(stepCur == 6)
{
	this.pg_rg.pg_rg.pg_1.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Result graphics open.");
}
//>> Open mnemo for KM101
else if(stepCur == 7)
{
	this.pg_2.pg_mn.pg_KM101.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Mnemo KM101 open.");
}
//>> Open graphics for KM101
else if(stepCur == 8)
{
	this.pg_2.pg_ggraph.pg_1.attrSet("pgOpen",true);
	this.attrSet("tipStatus","Graphics ΚΜ101 open.");
}
//>> Open PID-control panel
else if(stepCur == 9)
{
	this.ownerSess().pg_control.pg_ElCadr.attrSet("pgOpenSrc",this.pg_1.pg_mn.pg_1.wdg_PC1.attr("path"));
	this.attrSet("tipStatus","The parameter PC_KRD1 control panel open.");
	stepTm = 1;
}
//>> Open PID-control page
else if(stepCur == 10)
{
	this.ownerSess().pg_control.pg_cntrRegul.attrSet("pgOpenSrc",this.ownerSess().pg_control.pg_ElCadr.attr("path"));
	this.attrSet("tipStatus","The regulator PC_KRD1 control panel open.");
}
//>> Setpoint restore for PC KRD1
else if(stepCur == 11)
{
	SYS.DAQ.BlockCalc.Anast1to2node_cntr.PC_ΚΠΔ1.sp.set(5.8);
	this.attrSet("tipStatus","The regulator PC_KRD1 setpoint restore.");
}
else { stepCur = -1; stepTm = 0; }


If there is no demo mode need to on the project page, the frame, turn off the button to start the demonstration and the field of control panels extend.

Using - Runtime

In the runtime mode, the user can select the desired from available signal object (Ctrl+1...0), select the type of presentation (Ctrl+M,G,C,V,D,R), make the quittance of alarms, and also cause the control panel for the the desired element. After choosing, the user is presented the mnemonic scheme or common frame in the mnemonic schemes container and control panel in the control panels container. Then the user can observe the state on mnemonic schemes and panels, as well as to the make actions provided by them.


Fig. 22 shows an example of this element in the runtime mode.


"Root page (SO)" widget in the runtime mode. (90 Кб)
Fig.22. "Root page (SO)" widget in the runtime mode.

13. Passport (cntrPasp)

Element, shown in Fig. 23, is provided for displaying the parameter's passport: detailed information, including code, description, units, alarm borders, etc. Document is generated entirely dynamically.

Using - Development

This element should be placed in a logical container of the project's tree. In development mode, the widget is a blank "Document", and therefore the only screen shot with this widget in the runtime mode of the project is provided. Linking with the parameter is made dynamically when you call "Passport" for the visual elements of the parameter.

Using - Runtime

Calling the passport is made from the visual elements of parameter, for example: by right click of the mouse on the element "analog parameter" (anShow) and on the field of the "element cadr" widget (ElCadr) . After a call the separate window of the widget-passport with a list of all properties and values of the parameter as a table is opened.


"Pasport" widget in the runtime mode 1. (20 Кб) "Pasport" widget in the runtime mode 2. (11 Кб)
Fig.23. "Passport" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
pName Parameter's name Address Input link Parametr|NAME Address to the parameter's name to refer to the parameter entirely and get all of its properties

14. Document panel (doc_panel)

Element, shown in Fig. 24, is used to manage documents and navigate through their histories. The element supports dynamic and archival documents.


"Document panel" widget in the development mode (7 Кб)
Fig.24. "Document panel" widget in the development mode.

Using - Development

This element should be placed in a logical panels' container of the project's tree. Linking with the parameter is dynamic when called from the document's element.

Using - Runtime

Call of the panel is made from elements of the document. The panel provides tools that are somewhat different for dynamic and archival documents.


For dynamic document the following tools are provided:


Archival document provides only navigation through documents in the archive by listing them, and display current and overall documents.


Fig. 25 shows examples of this element in the runtime mode: dynamic (left) and archival (right).


"Document panel" widget in the runtime mode (11 Кб)
Fig.25. "Document panel" widget in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
Dinamic document
time Document time DateTime Full link <page>|time
bTime Document begin DateTime Full link <page>|bTime
doc Document String Full link <page>|doc
Archive document
n Archive size Integer Full link <page>|n
vCur View cursor Integer Full link <page>|vCur
aCur Archive cursor Integer Input link <page>|aCur
aSize Archive size Integer Input link <page>|aSize

15. Graphics group panel (grph_panel)

Element, shown in Fig. 26, serves to control the "Diagram" widget, it allows you to view trends' history for the required period of time and the desired resolution, the scale, the selection of archiver for display and there are supported trends' presentation in a range of present frequencies or XY.


"Graphics group panel" widget in the development mode (16 Кб) "Graphics group panel" widget in the runtime mode (15 Кб)
Fig.26. "Graphics group panel" widget in the development and runtime modes (left to right).

Using - Development

This element should be placed in the logical container of the project's tree. Linking with the parameter is dynamic when called from a diagram element.

Using - Runtime

Calling the panel is made from the diagram elements. The panel provides the following tools:

Linking attributes

IDParameterData typeConfigConfig templateDescription
tSek Trend time DateTime Full link <page>|tSek
tSize Trend size Real Full link <page>|tSize Temporal size of the trend in the history from the time of the trend.
trcPer Trace period Integer Full link <page>|trcPer Renewal period of the trend.
type Type Integer Full link <page>|type Trend's type: "Graph", "Spectrum of frequencies", "XY".
valArch Archiver String Full link <page>|valArch
curSek Cursor DateTime Full link <page>|curSek Time of the cursor.
curUSek Cursor, usec Integer Full link <page>|curUSek Time of cursor, microseconds.
sclVer Vertical scale Real Full link <page>|sclVerScl The percentage of vertical scale.
sclVerOff Vertical scale offset Real Full link <page>|sclVerSclOff Percentage of the offset on the vertical scale.
sclHor Horizontal scale Real Full link <page>|sclHorScl The percentage of horizontal scale.
sclHorOff Horizontal scale offset Real Full link <page>|sclHorSclOff Percentage of the offset on the horizontal scale.
sclWin Scale by window Boolean Full link <page>|sclWin Switching to the scaling by window mode.
sclWinCtx Scale: by window save context Object Input link <page>|sclWinCtx The context of saving of the original scale parameters for return.

16. Terminator panel (terminator)

Element, shown in Fig. 27, serves to fill the empty place when no item is selected for control.


"Terminator panel" widget. (3 Кб)
Fig.27. "Terminator panel" widget.

Using - Development

This element should be placed in the logical container of the project's tree.

Using - Runtime

Calling the panel is made from root page "RootPgSo" by changing the signal object or presentation mode.

17. Prescription: editing (prescrEdit)

The element "Prescription: editing", shown in Fig. 28, is one of the group frames for working with the prescriptions, which serves for the user-editing of prescription-programs.


The prescription-program is a sequentially call of the function's blocks — commands (macros), taking up to five arguments and return string, with result code at begin: "Working" (0), "Finished" (> 0) and "Error" (<0). Calling the step command is made in a loop until the "Working" (0) result is returned. Jump to the next step is made in the case of "Finished" (> 0) result and command "Pass" (2). In the case of error, the "Error" (<0) result, the execution of the prescription is terminated. Prescription's execution making through prescription controller's parameter, which support two mode of prescriptions execution:

  1. direct into the prescription controller object by commands stored into table "PrescrComs";
  2. by commands placed in view parameters of the logical controller account it's context, if the logical controller assigned into the prescription controller.

Macro-commands, which user can choose during the formation of a prescription-program, are formed by the programmer of SCADA-system under the specific application area by editing the commands table in the OpenSCADA or parameters list of selected logical controller. Table of commands is placed to the accessible in the specific OpenSCADA configuration database. As an example, this table is placed to the database of the library with the name "PrescrComs". Table of command has the following structure PrescrComs = (name, proc, arg1, arg2, arg3, arg4, arg5), where:


The several commands with the following names are reserved for special purposes:


The commands-parameters of the logical controller firming as template of parameters of subsystem "Data acquisition", which next used into the logical controller of prescription include mandatory, service and internal attributes:


Feature of using the commands-parameters is independent execution and possibility left some commands into background execution, regulators for example.


In the prescription-program formation process through the frame you are working with a table of programs. As an example, this table is placed in the database of the library with the name "PrescrProgs". The table of the programs has the following structure:
PrescrProgs = (name, prgTxt), Where:


The "Prescription: editing" frame contains from left to right:


The "Prescription: editing" frame in the development mode. (32 Кб)
Fig.28. The "Prescription: editing" frame in the development mode.

Using — Development

This frame should be placed in the mnemonic schemes or panels logical container of the project's tree.


For correct working of the frame it is necessary to copy an existing tables "PrescrComs" (if the commands mode is not into logical controller) and "PrescrProgs" from the database of the library to the desired database or create a new empty tables there by SQL the commands in the desired DB, for example SQLite:


Blank or copied commands table must be edited and filled with necessary commands in the DB "Table" page, if used first mode of commands, or the logical controller assigned, with commands list, into object of the prescription controller for second mode.


After formation of the tables it is necessary in the links of the frame to set the values of the database with tables and the names of tables themselves, specify the name of the export/import file and set link to object of prescription controller.

Using — Runtime

In the runtime mode, the user can add new prescription-programs, delete, copy and export the existing ones as well as to import prescriptions from other OpenSCADA stations. In the selected prescription-program user can do: add or insert a new step, removing or reposition the selected step. For the selected step of the prescription-program the user can set the command and enter values for the available parameters-arguments of the selected command, and then to keep changes of the step.


Fig. 29 shows an example of a frame at runtime.


The "Prescription: editing" frame in the runtime mode. (37 Кб)
Fig.29. The "Prescription: editing" frame in the runtime mode.

Linking attributes

IDParameterData typeConfigConfig templateDescription
Generic configuration
dbDB DB:Database String Constant DB DB address with tables in view {DBType}.{DBName}.
dbProgs DB:Programs String Constant DB Prescriptions-programs table name.
fileExpImp Export/import file String Constant File User's prescriptions-programs file for Export/Import.
Linking to prescription controller. The prescription controller realization example you can see into DB Dynamic model "AGLKS"
prExtComLs The list of available commands of prescription Object Input link Controller|comLs

18. Prescription: runtime (prescrRun)

The element "Prescription: runtime", shown in Fig. 30, is one of the group frames for working with the prescriptions, which serves to direct execution of programs-prescriptions or observe for execution into external program-prescription executor, previously formed in the Prescription: edit frame.


The "Prescription: runtime" frame contains from left to right:


The executable prescription-program may be suspended by pressing the "Pause" button or interrupted by pressing the "Stop" one. Also possible skip step by place to button "Skip" into step execution time.


On the any completion of the prescription-program the message with the parameters of the session is generated, and archiving of the session's document is made. Message with the parameters of a session can be used during viewing the message's archive, or to generate a list of sessions, for example, in the graphics group to go to the history for the session's time. To view the reports history of program's execution you can click on the document and browse on the appearing on the right navigation bar on archival document. By default, the archive of documents is set to the depth of 10 documents.


In addition to full-format frame of prescription execution also provided the simplified, which allow compact control and follow for the prescriptions execution as parts for other frames of a technological process (Fig.30).


The full-format and simplified "Prescription: runtime" frames in the development mode. (28 Кб)
Fig.30. The full-format and simplified "Prescription: runtime" frames in the development mode.

Using — development

This frames should be placed in the mnemonic schemes or panels logical container of the project's tree, for full-format, and to mnemo for simplified.


In the links of the frames it is necessary to set the database with the tables and the name of programs' table themselves as in the Prescription: editing, and also link to controller of prescriptions, like to Prescription: editing.


To provide the possibility of finished sessions archiving while the operator switches to another frame, it is necessary for the full-format frame in the project's tree to set the "Page: process not opened."

Using — Runtime

At the runtime mode the user can select the desired prescription-program and run-on execution and then track the execution progress or switch to other frames. Executable program you can pause by pressing the "Pause" button or terminate by pressing "Stop". Thereto you can skip current step execution by press button "Skip". Also the user can review or print reports of previously executed prescriptions, full-format frames, for what it is necessary to press the left mouse button on the document and browse on the navigation bar through the archive of executable prescriptions.


Fig. 31 shows an example of the full-format and simplified frames at runtime mode.


The full-format and simplified "Prescription: runtime" frames in the runtime mode. (54 Кб)
Fig.31. The full-format and simplified "Prescription: runtime" frames in the runtime mode.

Linking parameters

IDParameterData typeConfigConfig templateDescription
Generic configuration
dbDB DB:Database String Constant DB DB address with tables in view {DBType}.{DBName}.
dbProgs DB:Programs String Constant DB Prescriptions-programs table name.
Linking to prescription controller. The prescription controller realization example you can see into DB Dynamic model "AGLKS"
prExtCurCom Controller:current command Integer Input link Controller|curCom
prExtMode Controller:mode Integer Full link Controller|mode
prExtProg Controller:program String Full link Controller|prog
prExtStartTm Controller:start Integer Input link Controller|startTm
prExtWork Controller:work Object Input link Controller|work

19. Acception (accept)

The "Acception" element, presented in Fig. 32 implements a simple operations' acception dialog. The element contains a message with a question and two buttons "Apply" and "Cancel". The dialogue, for example, is used in the frame Prescription: editing to accept the deleting operation.


The "Accept" frame in the development and runtime mode. (18 Кб)
Fig.32. The "Accept" frame in the development and runtime mode.

Using - development

This widget can be used by the developer to create dynamic interaction frames in operations that require acception by the user. To use it you should add this item to the panels' logical container of the project's tree. For interaction this widget is opened by the frame-initiator the result of it is dynamic linkage of the dialogue with the "event" and "mess" attributes of the frame-initiator. The question message is taken from the "mess" attribute, and the "dlg_Apply" signal is transmitted to the "event" at acception.


Using - Runtime

Calling the dialogue is made from the frame-initiator, and closing is made by pressing any button of the dialog. If you click the "Apply" button the "dlg_Apply" signal will be sent to the frame-initiator, by which it can perform the desired actions.

Linking parameters

IDParameterData typeConfigConfig templateDescription
elEvent Element:event String Full link <page>|event It is used to send the "dlg_Apply" event if accepted.
elMess Element:message String Input link <page>|mess Source of the question message in the dialogue.

20. Graph's param select (graphSelPrm)

The "Selecting graph's parameter", shown in Fig. 33, implements the dialog to select the data source, often the archive ones, for the formation of the trend in the "Graphics group" frame. Selection is provided from the list, specified in the attribute "Available parameters for selection (allowSelLst)" of the frame-initiator. For the selected source you can specify the name, scale, dimension and the color of the trend.


In the "Available parameters for selection (allowSelLst)" attribute the data sources should be placed in the following way:


Example of the "Available parameters for selection (allowSelLst)" attribute's contents:


The "Graph's param select" in the development and runtime mode. (64 Кб)
Fig.33. The "Graph's param select" in the development and runtime mode.

Using - development

This frame should be placed to the panels' logical container of the project's tree. The "Available parameters for selection (allowSelLst)" attribute must be defined with the list of sources according to the rules described above in the "Graphics groups", which should provide the selection of the source by the user. As a result, the "Select" item will appear in the context menu of the Graphics group element.

Using - Runtime

Calling the dialogue is made by the "Select" item of the the Graphics group element context menu. The dialogue provides the user the possibility of selection the data source from the list, as well as an indication of its basic parameters: name, scale, dimension, and color of the trend. When you accept the dialogue the selected parameters are applied to the graphics group element chart, replacing the links. An empty item selection and applying causes to clean all the links and the graph's item. Into a text field under the list you can rapidly find any needed parameter.


 
Files[Hide files/form]
2012-03-23 09:19:13    (18 Kb)  accept.png The "Accept" frame in the development and runtime mode.
2011-01-26 16:07:22    (1 Kb)  anshow1d.png "Analog show 1" widget in the development mode
2011-01-26 16:07:41    (1 Kb)  anshow1r.png "Analog show 1" widget in the runtime mode
2011-01-26 16:08:01    (2 Kb)  anshowd.png "Analog show" widget in the development mode
2011-01-26 16:08:16    (2 Kb)  anshowr.png "Analog show" widget in the runtime mode
2011-01-26 16:08:44    (20 Kb)  cntrpaspr_1.png "Pasport" widget in the runtime mode 1.
2011-01-26 16:08:52    (11 Kb)  cntrpaspr_2.png "Pasport" widget in the runtime mode 2.
2011-01-26 16:09:17    (35 Kb)  cntrreguld.png "Regulator's control panel" widget in the development mode.
2011-01-26 16:09:34    (49 Kb)  cntrregulr.png "Regulator's control panel" widget in the runtime mode.
2011-03-11 17:19:11    (7 Kb)  doc_paneld.png "Document panel" widget in the development mode
2011-12-03 17:51:23    (11 Kb)  doc_panelr.png "Document panel" widget in the runtime mode
2013-06-27 11:57:46    (38 Kb)  elcadr.png "Element cadr" widget in the runtime mode.
2013-06-27 11:50:18    (16 Kb)  elcadrd.png "Element cadr" widget in the development mode.
2011-01-26 16:03:37    (2 Kb)  elviewcadrd.png "Views page's element" widget in the development mode.
2012-03-22 17:19:39    (5 Kb)  elviewcadrr.png "Views page's element" widget in the runtime mode.
2011-01-26 16:04:14    (2 Kb)  elviewgraphd.png "Graphics group element" widget in the development mode.
2011-04-11 11:58:09    (6 Kb)  elviewgraphr.png "Graphics group element" widget in the runtime mode.
2016-10-07 12:28:21    (64 Kb)  graphselprm.png The "Graph's param select" in the development and runtime mode.
2013-06-27 11:58:53    (30 Kb)  grpcadrd.png "Contours group" widget in the development mode.
2013-06-27 12:04:32    (36 Kb)  grpcadrr.png "Contours group" widget in the runtime mode.
2012-03-22 17:29:05    (16 Kb)  grpgraphd.png "Graphics group" widget in the development mode.
2012-03-22 17:30:19    (25 Kb)  grpgraphr.png "Graphics group" widget in the runtime mode.
2016-10-07 11:37:48    (16 Kb)  grph_paneld.png "Graphics group panel" widget in the development mode
2016-10-07 11:39:41    (15 Kb)  grph_panelr.png "Graphics group panel" widget in the runtime mode
2013-06-27 12:07:07    (32 Kb)  prescreditd.png The "Prescription: editing" frame in the development mode.
2013-06-27 12:08:48    (37 Kb)  prescreditr.png The "Prescription: editing" frame in the runtime mode.
2013-06-16 18:15:58    (28 Kb)  prescrrund.png The full-format and simplified "Prescription: runtime" frames in the development mode.
2013-06-16 18:21:13    (54 Kb)  prescrrunr.png The full-format and simplified "Prescription: runtime" frames in the runtime mode.
2011-01-26 16:04:46    (23 Kb)  resultgraphd.png "Result graphics" widget in the development mode.
2011-01-26 16:05:16    (4 Kb)  resultgrapheld.png "Result graphic's element" widget in the development mode.
2011-01-26 16:05:32    (4 Kb)  resultgraphelr.png "Result graphic's element" widget in the runtime mode.
2011-01-26 16:05:45    (27 Kb)  resultgraphr.png "Result graphics" widget in the runtime mode.
2012-03-22 17:32:41    (43 Kb)  rootpgsod.png "Root page (SO)" widget in the development mode.
2013-06-27 12:05:50    (90 Kb)  rootpgsor.png "Root page (SO)" widget in the runtime mode.
2011-01-26 16:13:56    (3 Kb)  terminatord.png "Terminator panel" widget.
2011-01-26 16:06:38    (12 Kb)  viewcadrd.png "Overview frames panel" widget in the development mode
2012-03-22 17:26:46    (12 Kb)  viewcadrr.png "Overview frames panel" widget in the runtime mode.
2011-04-11 13:45:49    (43 Kb)  wlb_main_en.odt The document in OpenSocument
Comments [Hide comments/form]