OpenSCADAWiki: Home Page En/Using/API Function Libs/ Lib User Prt Devs ...
This is an old revision of HomePageEn/Using/APIFunctionLibs/LibUserPrtDevs from 2017-06-02 12:22:59..
Ukrainian (1 Kb) Óêðà¿íñüêà?
Russian (1 Kb) Ðóññêàÿ?
 (2 Kb) Needs to translation
User protocol based library
Founded: January 2010
Version: 1.8
State: Free (GPL2 by default)
Author: Roman Savochenko
Description: Library of functions for provide access to data of different network devices with most simply protocols like to wide resources counters.
Address: DB in file: SQLite.LibDB.tmplib_DevLib and SQLite.LibDB.UserProtocol_uPrt (oscadalibs.db.gz)
Compatibility: OpenSCADA >= 0.9
About the library
The templates library "DevLib" is created to provide common templates and related functions for custom access to wide range of devices' data with simple protocol to implement into User Protocol module, present complex protocols (ModBus, OPC_UA, HTTP) or direct at internal language and also for some integration the devices data.
The template's names and it's parameters are available in languages: English, Ukrainian and Russian. Source code wrote into language independent mode with calls for the translations by function tr() and the message's translation also allowed for English, Ukrainian and Russian.
To connect the library to the project of the OpenSCADA station it is possible by downloading the attached file of the database, placing it in in the database directory of the station's project and creating the database object for the DB module "SQLite", indicating the database file in the configuration.
To use the templates at generic you need create the device representing object into module of Logical controller and select proper template from the templates library. Next follow to specific for the template into individual description to correct configuration.
In general the custom accessing conception to the device's data we can imagine like to figure 1.
Custom accessing to device's data conception. (21 Kb)
Fig.1. Custom accessing to device's data conception.
As you can see from image 1 intermediate to the device carried out through some transport by the device physical base. Requests to the transport you can send:
For placing here a protocol you need do next and follow to shown demands:
1. SMS (SMS)
Description: Provides operations with SMS by the GSM-modem connected as a serial device. For now supported only sending SMS messages to a number of remote cell phone or GSM modem. For sending supported: ECHO disable, PIN check and set, send in PDU and Text mode.
Author: Roman Savochenko <rom_as@oscada.org>
Version: 2.1
Output user protocol's XML request structure: <{cmd} pin="1111" tel="+380XXXXXXXXX" text="{0|1}" err="1:Error">{SMSText}</cmd>
cmd — command, for now only "send" allowed;
pin — PIN code to the SIM card access;
tel — telephone number for receiver (remote cell phone or GSM modem);
text{0,1} — SMS in the text mode, only ASCII
SMSText — the message text;
err — sets for the request result.
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "SMS", one transport allowed for more receivers.
  2. Set proper address, only for Serial device. The serial port speed, asynchronous data format and timeouts will adjusted by the function.
  3. Place some commands requests direct to present or new internal OpenSCADA procedures like:
  4. Result: Into variable rez you will get "OK" if no errors occur and the messages transmitted to the receiver.
2. SMTP (SMTP)
Description: Provides operations with EMail by its send through TCP-Socket or SSL. For now supported: TCP, SSL, AUTH, topic encoding for UTF-8.
Version: 1.1
Output user protocol's XML request structure: <send auth="{user}:{pass}" from="{FromAddr}" to="{ToAddr}" topic="{My Topic}" err="1:Error">{MessageText}</send>
topic — the message topic;
from — sender address;
to — destination address of the receiver;
auth — authenticate user and password;
MessageText — the message text;
Using/configuring:
  1. Create an output transport type "Sockets" or "SSL" and set ID that like "SMTP", one transport allowed for more receivers.
  2. Set proper address, for Sockets(25) or SSL(465). The transport's timeouts will adjusted by the function.
3. UPS (UPS)
Description: Uninterruptible power supply unifying data for provide all the data into single attribute of object type "All items" for next the control as the object with the data provide as table, alarming and allowing set writable attributes. The template aimed for using with module "System" data source as "UPS" and widget "Main.objProps" as the data presenter. The template also you can use as example for create like other data unification as complex object with properties, alarming and writing.
Version: 1.2
Template parameters:
ID Parameter Type Mode Attribute Configure Value
srcAddr Source object's address String Input Not attribute Constant
items All items Object Output Full access Variable
this The object Object Input Not attribute Variable
SHIFR Code String Input Not attribute Variable
NAME Name String Input Not attribute Variable
DESCR Description String Input Not attribute Variable
Using/configuring:
  1. Create a controller object into module "System" and set ID that like "SYSData".
  2. Create a parameter object into previous new the controller object and set ID that like "UPS".
  3. Create and start a logical controller object or use any present with need scheduling properties.
  4. Create a logical parameter object and select the template for that, one for each the devices. Enable the parameter.
  5. Into tab "Template configuration" of the logical parameter object you need set:
    • Source object's address — to address the UPS parameter object like "System.SYSData.UPS".
  6. Result: Into attribute items you will get the object with all attributes and its properties. At some violations into attribute "err" you will get the information.
  7. Into visual interfaces developing of Vision place widget "Main.objProps" to any page and link it to the parameter object crated into stage 4.
  8. Result: Into runtime the page you get table with data of the object, notifications about violations into the header and allowing for set writable properties.
4. Elemer TM510x (TM510x)
Description: Multichannels thermometer Elemer TM5102 and TM5103 of firm Elemer.
Version: 1.0
Output user protocol's XML request structure: <mess addr="1" err="1:Error">{req}</mess>
req — request/respond data;
addr — remote station address (1...254);
transport Transport String Input Not attribute Constant tm510x
addr Device address (1...254) Integer Input Not attribute Constant 1
devTp Device type Integer Input Read only Variable
errors Errors String Input Read only Variable
in1 Input 1 Real Input Read only Variable
in2 Input 2 Real Input Read only Variable
in3 Input 3 Real Input Read only Variable
in4 Input 4 Real Input Read only Variable
in5 Input 5 Real Input Read only Variable
in6 Input 6 Real Input Read only Variable
in7 Input 7 Real Input Read only Variable
in8 Input 8 Real Input Read only Variable
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "tm510", one for each the devices' used serial bus.
  2. Set proper the address and the timeouts to the Serial device.
    • Transport — to ID of the transport into stage 1.
    • Device address — to the device's logical address in bus by upper transport.
  6. Result: The logical parameter object will perform interaction and place gathered data to the parameter attributes.
5. EDWARDS TURBOMOLECULAR PUMPS (SCU750)
Description: Typical EDWARDS TURBOMOLECULAR PUMPS (http://edwardsvacuum.com) data request by SCU750 Cotrol Unit protocol.
Sponsored: Vasiliy Grigoriev from "Vacuum technologies laboratory (http://e-beam.ru)".
Version: 1.0
addr — remote station address (<0 - single; >=0 - multi port);
transport Transport String Input Not attribute Constant SCU750
addr Device address (-1...255) Integer Input Not attribute Constant 1
perGet Period data getting (s) Real Input Not attribute Constant 10
version Version String Input Read only Variable
snCntrUnit Serial number: Control Unit String Input Read only Variable
snPump Serial number: Pump String Input Read only Variable
cntPumpHour Pump hour counter (minutes) Real Input Read only Variable
cntCntrUnitHour Control unit hour counter (minutes) Real Input Read only Variable
cntStart Start counter Real Input Read only Variable
operMode Pump Operation Mode String Input Read only Variable
events Events String Input Read only Variable
tTMS TMS temperature (°Ñ) Integer Input Read only Variable
tMotor Motor temperature (°Ñ) Integer Input Read only Variable
rotSpeed Rotational speed (HZ) Integer Input Read only Variable
comStart Command: START Boolean Input Full access Variable
comStop Command: STOP Boolean Input Full access Variable
comReset Command: RESET Boolean Input Full access Variable
spSpeed Set point: Speed Integer Input Full access Variable
spTMSt Set point: TMS temperature Integer Input Read only Variable
spSpeedPrev Set point: Speed (previous) Integer Output Not attribute Variable
cnt Counter Integer Output Not attribute Variable
operModes Operation modes Object Output Not attribute Variable
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "SCU750", one for each the devices' used serial bus.
    • Period data getting — to need acquisition period which more to real processing by the logical level controller. Commands and some other will process immediate.
  6. Result: The logical parameter object will perform interaction and place gathered data to the parameter attributes. Also you allowed for send some commands to the device through writable attributes.
6. Heat counter computer VKT7 (VKT7)
Description: Firm "Teplocom" (http://www.teplocom.spb.ru) computer "VKT-7" for complex heat measurement and the count. The device complex enough by provide more parameters, more history to its and access by nonlinear Serial-based protocol at low speed. The template implement acquisition for all significant parameters, get history by hours, days and result months. Also you can simple enough append for process other left parameters.
Sponsored: Vladislav Chubuk
Version: 1.0
addr — remote station address (0...254);
imit Imitation drift % (0-disable) Real Input Not attribute Constant 0
trAddr Transport String Input Not attribute Constant Transport.Serial.out_VKT7
arhH Archiver: hours String Input Not attribute Constant
arhD Archiver: days String Input Not attribute Constant
arhRes Archiver: results-month String Input Not attribute Constant
maxDayDepth Archiver: maximum read depth for no hours archiver, days Integer Input Not attribute Constant 366
lastResTm Last result months read time (s) Integer Output Full access Variable 0
leftResTm Left result months for read from archive Integer Output Read only Variable
lastDTm Last days read time (s) Integer Output Full access Variable 0
leftDTm Left days for read from archive Integer Output Read only Variable
lastHTm Last hours read time (s) Integer Output Full access Variable
leftHTm Left hours for read from archive Integer Output Read only Variable
diffTm Difference time (server-counter), hours Integer Input Read only Variable
firmVer Firmware version Real Input Read only Variable
abonId Subscriber ID String Input Read only Variable
repDay Report day Integer Input Read only Variable
netNum Network number Integer Input Read only Variable
modelImpl Model implementation Integer Input Read only Variable
tTypeM t: dimension String Input Read only Variable
GTypeM G: dimension String Input Read only Variable
VTypeM V: dimension String Input Read only Variable
MTypeM M: dimension String Input Read only Variable
PTypeM P: dimension String Input Read only Variable
QoTypeM Qo: dimension String Input Read only Variable
QntTypeHIM ÂÍÐ: dimension String Input Read only Variable
QntTypeM ÂÎÊ: dimension String Input Read only Variable
t1_1 t1 (Tâ1) Real Input Full access Variable
t2_1 t2 (Tâ1) Real Input Full access Variable
t3_1 t3 (Tâ1) Real Input Full access Variable
V1_1 V1 (Tâ1) Real Input Full access Variable
V2_1 V2 (Tâ1) Real Input Full access Variable
V3_1 V3 (Tâ1) Real Input Full access Variable
M1_1 M1 (Tâ1) Real Input Full access Variable
M2_1 M2 (Tâ1) Real Input Full access Variable
M3_1 M3 (Tâ1) Real Input Full access Variable
P1_1 P1 (Tâ1) Real Input Full access Variable
P2_1 P2 (Tâ1) Real Input Full access Variable
Mg_1 Mg (Tâ1) Real Input Full access Variable
Qo_1 Qo (Tâ1) Real Input Full access Variable
Qg_1 Qg (Tâ1) Real Input Full access Variable
dt_1 dt (Tâ1) Real Input Full access Variable
BNR_1 ÂÍÐ (Tâ1) Real Input Full access Variable
BOC_1 ÂÎÑ (Tâ1) Real Input Full access Variable
G1_1 G1 (Tâ1) Real Input Full access Variable
G2_1 G2 (Tâ1) Real Input Full access Variable
t1_2 t1 (Tâ2) Real Input Full access Variable
t2_2 t2 (Tâ2) Real Input Full access Variable
t3_2 t3 (Tâ2) Real Input Full access Variable
V1_2 V1 (Tâ2) Real Input Full access Variable
V2_2 V2 (Tâ2) Real Input Full access Variable
V3_2 V3 (Tâ2) Real Input Full access Variable
M1_2 M1 (Tâ2) Real Input Full access Variable
M2_2 M2 (Tâ2) Real Input Full access Variable
M3_2 M3 (Tâ2) Real Input Full access Variable
P1_2 P1 (Tâ2) Real Input Full access Variable
P2_2 P2 (Tâ2) Real Input Full access Variable
Mg_2 Mg (Tâ2) Real Input Full access Variable
Qo_2 Qo (Tâ2) Real Input Full access Variable
Qg_2 Qg (Tâ2) Real Input Full access Variable
dt_2 dt (Tâ2) Real Input Full access Variable
BNR_2 ÂÍÐ (Tâ2) Real Input Full access Variable
BOC_2 ÂÎÑ (Tâ2) Real Input Full access Variable
G1_2 G1 (Tâ2) Real Input Full access Variable
G2_2 G2 (Tâ2) Real Input Full access Variable
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "VKT7", one for each the devices.
  5. Create or use a minutes (current) value archivator object (1m, period=60sek.).
  6. Create a hours value archivator object (arhH, period=3600sek.), days value archivator object (arhD, 86400sek.) and result month value archivator object (arhM, 86400sek.). Set "Period archiving (sec)" property of the archivators to '0' for disable the data flow from the archive buffer.
  7. Into tab "Template configuration" of the logical parameter object you need set:
    • Imitation drift % — to '0' for the imitation disable.
    • Transport — to path of the transport into stage 1, like "Transport.Serial.out_VKT7".
    • Archiver: hours — to the hours archiver into stage 6, like "FSArch.arhH".
    • Archiver: days — to the days archiver into stage 6, like "FSArch.arhD".
    • Archiver: results-month — to the result month archiver into stage 6, like "FSArch.arhM".
    • Archiver: maximum read depth for no hours archiver, days — to need for read no hours archives depth, in days.
  8. Into tab "Archiving" set archiving for needs attributes to the archivators.
  9. Result: The logical parameter object will perform interaction and place current gathered data to the parameter attributes and current archive. Other archives' data will read parallel from previous set depth by one value for period i.e. one day for minute period for days up to the current and last value.
7. Sycon Multi Drop Protocol (SMDP)
Description: STM devices for resonant frequency measurement for mass of deposited films attached to its surface by Sycon Instruments, Inc. (http://www.sycon.com).
Version: 1.0
Output user protocol's XML request structure: <mess addr="16" try="1" err="1:Error">{req}</mess>
addr — remote device address [16...254];
try — tries for the request;
transport Transport String Input Not attribute Constant SMDP
addr Device address (16...254) Integer Input Not attribute Constant 16
version Firmware Version String Input Read only Variable
CfgPrmSSID Configuration parameter session ID Integer Input Read only Variable
Srlno Measurement serial number Integer Input Read only Variable
RawFreq Channel freq. Real Input Read only Variable
GoodFreq Last used, good channel freq. (Hz) Real Input Read only Variable
RawThick Computed raw thickness, from frequency. (A) Real Input Read only Variable
XtalThick Computed material related thickness, can be zeroed. (A) Real Input Read only Variable
XtalThick_F Filtered computed material related thickness, can be zeroed. (A) Real Input Read only Variable
XtalRate Rate, angstroms per second. Real Input Read only Variable
XtalRate_F Rate, angstroms per second, filtered. Real Input Read only Variable
XtalLife XtalLife (%) Real Input Read only Variable
XtalQual Quality level (0-9). Integer Input Read only Variable
XtalQualPeak Highest quality level seen (0-9). Integer Input Read only Variable
XtalStab Stability level (0-9). Integer Input Read only Variable
XtalStabPeak Highest stability level seen (0-9). Integer Input Read only Variable
XtalStat Channel status. String Input Read only Variable
XtalLife_C XtalLife (%). Integer Input Read only Variable
SessId Session ID Integer Input Full access Variable
Fq Xtal start freq. (Hz) Real Input Full access Variable
Fm Xtal min freq. (Hz) Real Input Full access Variable
Density Material density (gm/cc). Real Input Full access Variable
Zratio Material Z ratio. Not scaled or unitized. Real Input Full access Variable
Tooling 1.000 is 100 % tooling (unity). Real Input Full access Variable
RateReq Requested rate (A/S). Real Input Full access Variable
QlvlTrip Quality threshold, if non 0 and exceeded, xtal fail occurs. Integer Input Full access Variable
SlvlTrip Stability threshold, if non 0 and exceeded, xtal fail occurs. Integer Input Full access Variable
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "SMDP", one for each the devices' used serial bus.
8. Power supply for turbomolecular pumps (TMH)
Description: Power supply for turbomolecular pumps of firm SHIMADZU, model EI-R04M.
Version: 1.0
addr — remote station address (1...32);
transport Transport String Input Not attribute Constant TMP
modelID Model ID String Input Read only Variable
I Current (A) Real Input Read only Variable
axle1disb Axle 1 disbalance Integer Input Read only Variable
axle2disb Axle 2 disbalance Integer Input Read only Variable
MP_X1 MP X1 Integer Input Read only Variable
MP_Y1 MP Y1 Integer Input Read only Variable
MP_X2 MP X2 Integer Input Read only Variable
MP_Y2 MP Y2 Integer Input Read only Variable
MP_Z MP Z Integer Input Read only Variable
operMode Operation Mode String Input Read only Variable
operCntr Operation Control Mode String Input Read only Variable
comInteract Interactive mode Boolean Input Full access Variable
comAutonom Autonomous mode Boolean Input Full access Variable
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "TMP", one for each the devices' used serial bus.
9. Temperature measurement IT-3 (IT3)
Description: Temperature measurement IT-3 from OmskEtalon.
Version: 1.2
transport Transport String Input Not attribute Constant IT3
addr Device address Integer Input Not attribute Constant 1
T Temperature Real Input Read only Variable
H Upper border Boolean Input Read only Variable
L Lower border Boolean Input Read only Variable
relSt Relay state Boolean Input Read only Variable
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "IT3", one for each the devices' used serial bus.
  2. Set proper the address and the timeouts to the Serial device, typical "{serDevPath}:4800:8N2".
10. IVE-452HS-02 (IVE_452HS_02)
Description: Power supply of beam-electrons evaporator of "Plasma Tech" Ltd, from Moskov.
Version: 1.0
Output user protocol's XML request structure: <mess addr="255" err="1:Error">{req}</mess>
addr — remote station address (0...255);
transport Transport String Input Not attribute Constant Sockets.out_IVE
addr Device address Integer Input Not attribute Constant 255
COIA Output current level set-point Integer Output Full access Variable
COUA Output voltage level set-point Integer Output Full access Variable
COPA Output power level set-point Integer Output Full access Variable
DIA Output current Integer Input Read only Variable
DUA Output voltage Integer Input Read only Variable
DPA Output power Integer Input Read only Variable
DFA Electric arcs frequency Integer Input Read only Variable
DAC Electric arcs counter Integer Input Read only Variable
COM_DEW Command: Blocking by SC and XX Boolean Input Full access Variable
COM_OUT Command: Display on UI out block's params Boolean Input Full access Variable
COM_DEP Command: Enable MK Boolean Input Full access Variable
COM_DEL Command: Blocks #1,2 to net Boolean Input Full access Variable
COM_UF Command: Display on UI frequency and current Boolean Input Full access Variable
DKW MUBR of the block overheated Boolean Input Read only Variable
DKZ Short circuits on the block out Boolean Input Read only Variable
DK MK of the block overheated Boolean Input Read only Variable
DE Power and voltage on out present Boolean Input Read only Variable
Using/configuring:
  1. Create an output transport type "Serial" direct, or by the Sockets gate and, set address that like "Sockets.out_IVE", one for each the devices' used serial bus.
    • Transport — to the address of the transport into stage 1. Supported tracing for the hot change.
    • Device address — to the device's logical address in bus by upper transport. Supported tracing for the hot change and real the device's address changing.
11. OPTRIS CT/CTL (OPTRIS)
Description: OPTRIS CT/CTL communication interface of "Optris" GmbH, from Berlin.
Version: 1.0
Output user protocol's XML request structure: <mess addr="1" cs="1" err="1:Error">{req}</mess>
addr — remote station address (0...15);
ñs — use control sum for SET commands [0,1];
transport Transport String Input Not attribute Constant Serial.out_OPTRIS
Tproc T process Real Input Read only Variable
Thead T head Real Input Read only Variable
Tbox T box Real Input Read only Variable
Tact T act. Real Input Read only Variable
eps IR epsilon Real Input Full access Variable
trans IR transmission Real Input Full access Variable
spIll Spot illumination Logical Input Full access Variable
Using/configuring:
  1. Create an output transport type "Serial" direct, or by the Sockets gate and, set address that like "Serial.out_OPTRIS", one for each the devices' used serial bus.
12. CTR 100, 101 (CTR)
Description: The RS232C Serial Interface permits the communication between the digital Oerlikon Leybold Vacuum CERAVAC, from Köln.
Version: 1.0
Output user protocol's XML request structure: <mess err="1:Error">{req}</mess>
transport Transport String Input Not attribute Constant Serial.out_CTR
press Pressure, Tor Real Output Read only Variable
zeroSet Zero set Logical Input Full access Variable
Using/configuring:
  1. Create an output transport type "Serial" direct, or by the Sockets gate and, set address that like "Serial.out_CTR", one for each the devices' used serial bus.
13. IEC-60870 (IEC60870)
Description: IEC 60870 part 5 is one from the IEC 60870 set of standards which defines systems used for telecontrol (supervisory control and data acquisition) in electrical engineering and power system automation applications. Part 5 provides a communication profile for sending basic telecontrol messages between two systems, which uses permanent directly connected data circuits between the systems. The template implements part 104 (Ethernet transport) for the client and followed services: STARTDT, STOPDT, TESTFR, Ack, C_IC_NA_1, C_CI_NA_1, C_SC_NA_1, M_SP_NA_1, M_ME_NB_1, C_CS_NA_1. To accumulation of the gathered and controlling data used an object into attribute "items" for next the control as the object with the data represent as table, alarming and allowing set the writable attributes. To the data control by attributes at once you can point its into the attribute "itemsSet". Into the template for the first time used the non request mode of an output transport and free attributes creation wile performing.
Version: 1.0
Sponsored: Ustijancev Michael.
Implementing task: http://oscada.org/en/development/tasks/posts/subsystem_daq/iec_60870_5_acquisition_protocol_implementation
transport Transport String Input Not attribute Constant Sockets.out_IEC60870
addr Address, {addr}.{OA} String Input Not attribute Constant 0.5
tmRetr Retry connection time, s Real Input Not attribute Constant 10
t1 Acknowledge lack timeout, s Real Input Not attribute Constant 1.5
t2 Acknowledge timeout, s Real Input Not attribute Constant 1
t3 Test timeout, s Real Input Not attribute Constant 2
k Maximum unconfirmed Integer Input Not attribute Constant 12
w Maximum no ack Integer Input Not attribute Constant 8
itemsSet Items set by: "ai|di|do:{IOA}[-{EndIOA}]:a[:{NameBase}]" Text Input Full access Variable
this Object Object Input Not attribute Variable
f_frq Function calculate frequency (Hz) Real Input Not attribute Variable 1000
f_start Function start flag Boolean Input Not attribute Variable 0
f_stop Function stop flag Boolean Input Not attribute Variable 0
f_err Function error String Input Not attribute Variable 0
Using/configuring:
  1. Create an output transport type "Sockets", set address to that like "Sockets.out_IEC60870", one for each the device-PLC.
  2. Set proper address and timeouts to the Sockets device-PLC.
  3. Create and start a logical controller object or use any present with need scheduling properties. For interaction by IEC-60870-104 you need set the execution period to no lesser then 100ms.
  4. Create a logical parameter object and select the template for that, one for each the devices-PLCs. Enable the parameter.
    • Address — data address in format "{addr}.{OA}".
    • Retry connection time — retry connection time in seconds at the connection lack.
    • Acknowledge lack timeout, in seconds.
    • Acknowledge timeout, in seconds.
    • Test timeout, in seconds.
    • Maximum unconfirmed — not used into the client but it is not generate like flow.
    • Maximum no ack — maximum input packages after what the client will send "Ack".
  6. Result: The logical parameter object will perform interaction and place gathered data to the object "items", create/place and check to commands for proper attributes, created by the "itemsSet" instruction.
14. Mercury 200 (m200)
Description: One phase counter of electricity Mercury 200, 203.2Ò, 206 from firm Incotex (http://www.incotexcom.ru)
Author: Arsen Zakojan <godzilla919@gmail.com>
Version: 1.0
Output XML request structure of user protocol: <req first="255" second="16777215" data="{req}">{resp}</mess>
req — request's data;
resp — respond's data;
first,second — first and three second bytes of the common address (0...4294967295).
Parameters of the template:
s Energy from reset, tariffs sum String Input Read only Variable
t1 Energy from reset, tariff 1 Real Input Read only Variable
t2 Energy from reset, tariff 2 Real Input Read only Variable
t3 Energy from reset, tariff 3 Real Input Read only Variable
t4 Energy from reset, tariff 4 Real Input Read only Variable
U Voltage U(V) Real Input Read only Variable
I Current I(A) Real Input Read only Variable
P Power P(W) Real Input Read only Variable
transport Transport String Input Not attribute Constant merc200
netaddr Network address Real Input Not attribute Constant 1
naladchik Coded address by the program Fixer+ Boolean Input Not attribute Constant 0
tarif Read energy from reset Boolean Input Not attribute Constant 1
UIP Read current values Boolean Input Not attribute Constant 1
first First byte of the address Integer Input Not attribute Variable
second Last 3 bytes of the address Integer Input Not attribute Variable
Using/configuring:
  1. Create an output transport type "Serial" with name like to "merc200".
  2. Set proper address and timeouts for the Serial device.
  4. Create an object of the logical parameter and select the template for this, one for each device. Enable the parameter.
  5. Into tab "Template configuration" of the object of the logical parameter you need to set:
    • Network address — the counter's logical address.
    • Coded address by the program Fixer+ — set the flag for counters coded by the program. Most likely the address will equal to apartment number.
    • Read energy from reset — set the flag if you need the data.
    • Read current values — set the flag to read current values.
15. Mercury 230 (m230)
Description: Three phase counter of electricity Mercury 230, 231, 232, 233, 234, 236 from firm Incotex (http://www.incotexcom.ru)
Version: 1.0
Output XML request structure of user protocol: <req netaddr="255" data="{req}">{resp}</mess>
netaddr — Network address. For counters Mercury 230, 231 and 233 the tree last digits are serial number or they are last two digits for the number more to 240. If the last numbers are zero, the network address is "1". Universal, broadcast address is "0".
answer Answer to the password request String Input Read only Variable
TS Read energy of tariffs sum Boolean Input Not attribute Constant 0
T1 Read energy of tariff 1 Boolean Input Not attribute Constant 0
T2 Read energy of tariff 2 Boolean Input Not attribute Constant 0
T3 Read energy of tariff 3 Boolean Input Not attribute Constant 0
T4 Read energy of tariff 4 Boolean Input Not attribute Constant 0
P Read power P Boolean Input Not attribute Constant 0
Q Read power Q Boolean Input Not attribute Constant 0
S Read power S Boolean Input Not attribute Constant 0
U Read voltage U Boolean Input Not attribute Constant 0
I Read current I Boolean Input Not attribute Constant 0
K Read power coefficient Boolean Input Not attribute Constant 0
F Read frequency F Boolean Input Not attribute Constant 0
N Read serial number Boolean Input Not attribute Constant 0
TSAp Energy from resetting, tariffs sum A+ Real Input Read only Variable
TSAm Energy from resetting, tariffs sum A- Real Input Read only Variable
TSRp Energy from resetting, tariffs sum R+ Real Input Read only Variable
TSRm Energy from resetting, tariffs sum R- Real Input Read only Variable
T1Ap Energy from resetting, tariff 1 A+ Real Input Read only Variable
T1Am Energy from resetting, tariff 1 A- Real Input Read only Variable
T1Rp Energy from resetting, tariff 1 R+ Real Input Read only Variable
T1Rm Energy from resetting, tariff 1 R- Real Input Read only Variable
T2Ap Energy from resetting, tariff 2 A+ Real Input Read only Variable
T2Am Energy from resetting, tariff 2 A- Real Input Read only Variable
T2Rp Energy from resetting, tariff 2 R+ Real Input Read only Variable
T2Rm Energy from resetting, tariff 2 R- Real Input Read only Variable
T3Ap Energy from resetting, tariff 3 A+ Real Input Read only Variable
T3Am Energy from resetting, tariff 3 A- Real Input Read only Variable
T3Rp Energy from resetting, tariff 3 R+ Real Input Read only Variable
T3Rm Energy from resetting, tariff 3 R- Real Input Read only Variable
T4Ap Energy from resetting, tariff 4 A+ Real Input Read only Variable
T4Am Energy from resetting, tariff 4 A- Real Input Read only Variable
T4Rp Energy from resetting, tariff 4 R+ Real Input Read only Variable
T4Rm Energy from resetting, tariff 4 R- Real Input Read only Variable
PS Power P(W) by the phases sum Real Input Read only Variable
P1 Power P(W) by the phase 1 Real Input Read only Variable
P2 Power P(W) by the phase 2 Real Input Read only Variable
P3 Power P(W) by the phase 3 Real Input Read only Variable
QS Power Q(var) by the phases sum Real Input Read only Variable
Q1 Power Q(var) by the phase 1 Real Input Read only Variable
Q2 Power Q(var) by the phase 2 Real Input Read only Variable
Q3 Power Q(var) by the phase 3 Real Input Read only Variable
SS Power S(VA) by the phases sum Real Input Read only Variable
S1 Power S(VA) by the phase 1 Real Input Read only Variable
S2 Power S(VA) by the phase 2 Real Input Read only Variable
S3 Power S(VA) by the phase 3 Real Input Read only Variable
U1 Voltage U(V) by the phase 1 Real Input Read only Variable
U2 Voltage U(V) by the phase 2 Real Input Read only Variable
U3 Voltage U(V) by the phase 3 Real Input Read only Variable
I1 Current I(A) by the phase 1 Real Input Read only Variable
I2 Current I(A) by the phase 2 Real Input Read only Variable
I3 Current I(A) by the phase 3 Real Input Read only Variable
KS Power coefficient by the phases sum Real Input Read only Variable
K1 Power coefficient by the phase 1 Real Input Read only Variable
K2 Power coefficient by the phase 2 Real Input Read only Variable
K3 Power coefficient by the phase 3 Real Input Read only Variable
F1 Frequency F(Hz) Real Input Read only Variable
N1 Serial number String Input Read only Variable
netaddr Network address (0...240) Integer Input Not attribute Constant 1
password Password String Input Not attribute Constant 111111
transport Transport String Input Not attribute Constant merc230
Using/configuring:
  1. Create an output transport type "Serial" with name like to "merc230".
    • Network address (0...240) — logical address of the counter.
    • Password — first level password, by default 111111.
    • Set flags for all parameters you need to read.
16. Example: DCON (DCON)
Description: Mostly aimed for example implement the user protocols into OpenSCADA and contains only main functions into the protocol part.
Input user protocol's part: Test implements only processing for requests '#' and '@' with fixed reply data.
Using/configuring:
  1. Create an input transport type mostly "Serial" and set any ID.
  3. Set transport protocol to "UserProtocol.DCON".
  4. Result: all requests to the input transports will process by input part of the module.
Output user protocol's XML request structure: <ReqSymb addr="1" err="1:Error">{req}</ReqSymb>
ReqSymb — request type symbol into the tag name, like: '#', '@', etc;
addr — remote host address [1...240];
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "DCON", one for each the devices' used serial bus.
  4. Result: Into variable data you will get the request's data part if no errors occur. The data is analog inputs' values.
17. Example: OWEN (OWEN)
Description: Mostly models of OWEN devices by specific protocol.
Author: Constantine (IrmIngeneer)
Refactoring: Roman Savochenko <rom_as@oscada.org>
Output user protocol's XML request structure: <mess addr="1" err="1:Error">{req}</mess> — message tag
addr — remote station address (0...2047);
Using/configuring:
  1. Create an output transport type "Serial" and set ID that like "OWEN", one for each the devices' used serial bus.
18. One Wire by {DS9097,DS9097U} (1W_{DS9097,DS9097})
Description: One Wire sensors bus implementing by 1Wire-adapter {DS9097,DS9097U}. Supported direct and parasite powering for the temperature sensors.
Supported 1Wire-devices: DS1820, DS1820/DS18S20/DS1920 (not tested), DS1822 (not tested), DS2413, DS2408, DS2450, DS2438.
Version: 1.1, 1.1
DS9097(U) (251 Kb)
transport Transport of the One Wire bus, Serial String Input Not attribute Constant oneWire
tmResc Rescan period, s Real Input Not attribute Constant 60
power Power, for temperature Boolean Input Read only Variable
Using/configuring:
  1. Create an output transport type "Serial", set address to that like "oneWire", one for each the One Wire bus.
  2. Set proper address, only for the adapter's serial device like "/dev/ttyS{N}". The serial port speed, asynchronous data format and timeouts will adjusted by the template.
  3. Create and start a logical controller object or use any present with the need scheduling properties.
  4. Create a logical parameter object and select the template for that, one for each One Wire bus. Enable the parameter.
    • Transport of the One Wire bus, Serial — to the address of the transport into stage 1. Supported tracing for the hot change.
    • Rescan period, s — periodicity of rescan to new and removed devices search.
  6. Result: The logical parameter object will perform at first searching to 1Wire devices on the bus and create included parameters to the each found one. Next the logical parameter object will perform gather data of the found devices and trace to modify of the writable device's properties.
19. I2C: PCF8591 (PCF8591)
Description: I2C 8-bit 4xA/D and D/A converter. Connect through a Serial output transport into the I2C mode.
Version: 1.0
transport Transport of the I2C, Serial String Input Not attribute Constant i2c
addr Device address [0...119] Integer Input Not attribute Constant 72
vRef Reference voltage, V Real Input Not attribute Constant 3.2
ai0 AI0 Real Input Read only Variable
ai1 AI1 Real Input Read only Variable
ai2 AI2 Real Input Read only Variable
ai3 AI3 Real Input Read only Variable
ao AO Real Input Full access Variable
Using/configuring:
  1. Create an output transport type "Serial", set address to that like "i2c", one for each the I2C bus.
  2. Set proper address, only the I2C bus address like "/dev/i2c-{N}". Set the symbol's time into the timeouts field to minimum value.
  4. Create a logical parameter object and select the template for that, one for each I2C slave device. Enable the parameter.
    • transport — to the address of the transport into stage 1. Supported tracing for the hot change.
    • addr — the I2C slave device's address [0...119].
    • vRef — reference voltage of the AIs and AO.
  6. Result: The logical parameter object will perform interaction and place gathered data to the AI attributes and also will take the AO and write to the chip.
20. I2C: PCF8574 (PCF8574)
Description: I2C 8-bit 8DIO. Connect through a Serial output transport into the I2C mode.
Version: 1.0
transport Transport I2C String Input Not attribute Constant i2c
addr Device address (0, 119) Integer Input Not attribute Constant 39
di0 DI0 Boolean Input Read only Variable
di1 DI1 Boolean Input Read only Variable
di2 DI2 Boolean Input Read only Variable
di3 DI3 Boolean Input Read only Variable
di4 DI4 Boolean Input Read only Variable
di5 DI5 Boolean Input Read only Variable
di6 DI6 Boolean Input Read only Variable
di7 DI7 Boolean Input Read only Variable
do0 DO0 Boolean Output Full access Variable
do1 DO1 Boolean Output Full access Variable
do2 DO2 Boolean Output Full access Variable
do3 DO3 Boolean Output Full access Variable
do4 DO4 Boolean Output Full access Variable
do5 DO5 Boolean Output Full access Variable
do6 DO6 Boolean Output Full access Variable
do7 DO7 Boolean Output Full access Variable
Using/configuring:
  6. Result: The logical parameter object will perform interaction and place gathered data to the DI attributes and also will take the DO and write to the chip.
21. I2C: BMP180 (BMP180)
Description: I2C Pressure and Temperature sensor. Connect through a Serial output transport into the I2C mode.
Version: 1.0
addr Device address [0...119] Integer Input Not attribute Constant 119
oss Oversampling setting (0...3) Integer Input Not attribute Constant 0
t T, °Ñ Real Input Read only Variable
p P, Pa Real Input Read only Variable
Using/configuring:
    • oss — oversampling setting of pressure measurement [0...3].
  6. Result: The logical parameter object will perform interaction and place gathered data to the Pressure and Temperature attributes.
22. I2C: DS3231 (DS3231)
Description: I2C RTC chip with Temperature sensor and calibration on it. Connect through a Serial output transport into the I2C mode.
Version: 1.0
tm Date and time, YYYY-MM-DDTHH:mm:SS String Input Full access Variable
agOff Aging offset, [-128...127] Integer Input Full access Variable
p32k Enable 32768Hz Boolean Input Full access Variable
pSQW Enable SQUARE-WAVE OUTPUT Boolean Input Full access Variable
pSQWf SQUARE-WAVE OUTPUT frequency: 0-1Hz, 1-1.024kHz, 2-4.096kHz, 3-8.192kHz Integer Input Full access Variable
Using/configuring:
  6. Result: The logical parameter object will perform interaction and place gathered data to the DateTime, Temperature and some one state attributes and also will take the DateTime, some one state attributes and write it to the chip.
23. I2C: AT24C{32|64} (AT24CXX)
Description: Provides operations with EEPROM memory based on I2C chips AT24C32 (4KB) and AT24C64 (8KB). Supported random reading and writing.
Version: 1.0
Output user protocol's XML request structure: <{cmd} addr="{ChipAddr}" off="{MemOffset}" size="{ReadSize}" err="1:Error">{ReadWriteSeq}</{cmd}>
cmd — command, for now there allowed: "read", "write";
addr — I2C device address [0...119];
off — memory part offset;
size — readed memory block size.
ReadWriteSeq — Read/Write bytes sequence.
Using/configuring:
  4. Result: Into text() for "read" you will get the read data if no errors occur.
24. GPIO: DHT11,22 (AM23XX) (DHT)
Description: Digital Temperature and Humidity Sensor for models: DHT11, DHT12, AM2302, AM2320, ... . The module designed for the sensors connect through GPIO, mostly it's Raspberry PI BCM2835 GPIO.
Conditions: Exclusively realtime planing in the priority 199 (FIFO-99).
Version: 1.0
addr GPIO address with functions mode(), get() and put(), mostly it's BCM2835 String Input Not attribute Constant DAQ.BCM2835.pi.pi
pin IO pin number of the GPIO Integer Input Not attribute Constant 17
tries Tries [1...5] Integer Input Not attribute Constant 2
dev Device (0-DHT11, 1-DHT22) Integer Input Not attribute Constant 1
h H, % Real Input Read only Variable
Using/configuring:
  1. Create an output controller and parameter object in DAQ module "BCM 2835", by default it's "pi.pi".
  2. Create and start a logical controller object or use any present with need scheduling properties (FIFO-199).
  3. Create a logical parameter object and select the template for that, one for each sensor. Enable the parameter.
  4. Into tab "Template configuration" of the logical parameter object you need set:
    • addr — To the address of the "BCM 2835" parameter like "DAQ.BCM2835.pi.pi". Supported tracing for the hot change.
    • pin — GPIO pin number where connected the data pin of the sensor.
    • tries — Tries of the sensor read.
    • dev — Generic device specific selection.
  5. Result: The logical parameter object will perform interaction and place gathered data to the Temperature and Humidity attributes.
25. GPIO|I2C: 1602A(HD44780) (1602A)
Description: LCD Module 1602A, STN, BLUB, 16 Character x 2 Line, 5 x 8 Dots, by the direct (Raspberry PI BCM2835 GPIO) or I2C (PCF8574) wiring.
Conditions: Default planing policy but realtime one preferred.
Version: 1.1
transport Transport of the I2C, Serial (i2c) or
GPIO address with function put(), mostly it's BCM2835 (DAQ.BCM2835.pi.pi)
addr I2C device address [0...119] Integer Input Not attribute Constant 39
RS GPIO Pin: Reset Integer Input Not attribute Constant 7
E GPIO Pin: Enable Integer Input Not attribute Constant 8
D4 GPIO Pin: Data4 Integer Input Not attribute Constant 25
D5 GPIO Pin: Data5 Integer Input Not attribute Constant 24
D6 GPIO Pin: Data6 Integer Input Not attribute Constant 23
D7 GPIO Pin: Data7 Integer Input Not attribute Constant 18
ln1 Line 1 String Input Full access Variable
ln2 Line 2 String Input Full access Variable
Using/configuring:
  1. Create an output controller and object of parameter in DAQ module "BCM 2835", by default it's "pi.pi" or create an output transport type "Serial", set address to that like "i2c", one for each the I2C bus.
  2. Create and start a logical controller object or use any present with need scheduling properties.
  3. Create a logical parameter object and select the template for that, one for each display. Enable the parameter.
    • transport — To the address of the "BCM 2835" parameter like "DAQ.BCM2835.pi.pi" or to the address of the transport into stage 1. Supported tracing for the hot change.
    • addr — The I2C slave device's address [0...119].
    • RS, E, D4, D5, D6, D7 — GPIO pins number where connected proper data ones of the sensor.
  5. Result: The logical parameter object will perform interaction and set lines' values to the display.
