As it can be seen in the section above, OpenSCADA allows configuration for execution in various roles. Support of this possibility is provided by the developed mechanisms for configuration and storage of configuration data. This section contains a description of these mechanisms, designed to demonstrate the flexibility and diversity, thereby allowing to use OpenSCADA to 100%.
In describing the configuration mechanisms and methods of its storage in this section it will be focused the description of system-wide mechanisms. Features of the configuration of modules of subsystems of OpenSCADA are provided in their own module's documentation.
In OpenSCADA it is used the formalized approach to describing the configuration interfaces based on XML. In fact, features of the component's configuration are provided by the component itself, thereby running through the whole system, as the nervous system of the organism. In terms of OpenSCADA it is called the interface of control of OpenSCADA (Control interface). On the basis of the control interface the graphical interfaces of the user configuration are generated by means of modules of OpenSCADA. This approach has the following important advantages:
In OpenSCADA the three configuration modules on the different basis of visualization are provided. Lets observe them and their configuration options:
Configuration values, changed in the configurators, as well as most of the data are stored in databases (DB). Given the modularity of subsystems "DB", there can be different database. Moreover, there is the possibility of storing different OpenSCADA parts in different databases of the same type and in the database of different types as well.
In addition to the database configuration information may be contained in the OpenSCADA configuration file, and passed through the command line parameter's when you call OpenSCADA. Saving the configuration in the configuration file is carried out on an equal footing with the database. Standard name of the OpenSCADA configuration file is /etc/oscada.xml. The format of the configuration file and command line parameters we'll examine in the separate section.
Some node's configuration changing will set the modification flag for the node, and also will set active for buttons "Load from DB", for loading the first configuration, and "Save to DB" for the changes saving. The modification flag also rise to parrent node, which allow for restore-save from root node, but real into operations with DB will participate only modified nodes.
A node removing causes to removing it from storage-DB and modification mechanism do not work for this operation.
Many of the settings and configuration objects OpenSCADA, which are executed or are already enabled, are not applied immediately, as for changes, because the configuration is read/apply usually only when turn on or start. Therefore to apply the changes, in such cases, it is enough to enable/disable enabled object or to restart the running start/stop. Presently many configurations, which its are not provided applying for now, just are not allowed for editing.
Further examining of the OpenSCADA configuration will be based on the interface of the configurator UI.QTCfg, but the principles of work will be fully consistent with the rest of the configurators owing to the generality in the control interface of OpenSCADA.
We will start examining with the configuration of system parameters of OpenSCADA, which is located in the six tabs at the root page of the station:
To modify the fields of this page it may be required the super user's rights. Get these rights you can by means of including your user into the superuser's group "root", or by entering the station from the superuser "root".
We must mention another one important point: the fields of the identifiers of all OpenSCADA objects are unacceptable for direct editing, because they are keys for storage of objects' data in the database. However, to change the object's identifier you can by the command of cutting and the further pasting of the object (Cut-> Paste) in the configurator.
The service task of the redundancy mechanism is always running and executed at intervals which are prescribed in the appropriate configuration field. The real work on implementing the redundancy is carried out in the presence of at least one redundant station in the list of stations, and implies:
There is recommended the redundancy configure in way for DBs of the redundant stations save equal and that will allow you to copy its painlessly to each the station and then to backup only one the DBs set. And the configurations specified to the different stations will save into the configuration file and you can simply configure and change the needed station by the proper configuration file select.
The redundancy configuration start from the redundant stations appending to list of system stations OpenSCADA in tab "Subsystem" of the subsystem "Transports" (Fig.4.3b). And to add here needs not only the redundant stations to the current one but the same current one with its external IP, that is some loop. Further this configurations will have been stored into the generic DB of the redundant system, and from this time the DBs will be used for that all redundant station creation. Then there is important to make on that stage all needed changes into the generic DB and about this project in general!
Next for the concrete station, with copy of the generic DB, we configure its specific parameters into the tab "Redundancy" of the main page (Fig.4c), which will be stored into the configuration file.
After that all next configurations of redundancy perform into the tab "Redundancy" of proper subsystem, "Data acquisition" (Fig.4.5b) or "Archives" (Fig.4.6b). If you will set the parameter "Local primary commands transfer" (Fig.4c) then the configurations, like to any other generic configurations, can be performed at any one from the stations and all the performed changes will be transferred to all other ones, sure if its are available.
For OpenSCADA different working specific debug you may be necessary to enable addition-debugging messages generation, which you can set by select minimal messages level, into tab "Station", to "Debug (0)". As a result of this will emerge tab "Debug" (fig.4e) where available the objects counters for control to leaks, and also the table with incoming debug messages' categories list. Into the table you can select only needed debug messages sources and omit to overload the archiving messages subsystem and overall the system performance decrease. You can also select higher categories, up to root system category, that will disable detailed selection and enable all messages generation by the level or by overall system. For the debug messages observing you need to go subsystem "Archives" (fig. 4.6c), and for this provided button "See to messages". Selected debug mode and debug categories list can be standard stored to configuration file and on next boot the debug mode will be activated, this important primarily for the objects counters.
While examining the configuration pages of modular subsystems there will be described the general for all modules properties. However, it should be noted that each module can provide both: the additional tabs, and separate fields for the configuration of their own functioning for the pages, objects of which are inherited by modules. Information on the features and additions of the modules can be found in separate documentation for each of them.
The subsystem is the modular one and contains a hierarchy of objects depicted in Figure 4.1a. To configure the subsystem the root page of the subsystem "DB" containing the tab "Modules". Tab "Modules" (Fig. 4.1b) contains the list of modules in subsystem "DB", available at the station.
To modify the page's fields of this subsystem it may be required the super user's rights or the inclusion of your user to the "DB" group.
Each module of the "DB" subsystem provides the configuration page with the following tabs: "DB" and "Module". "DB" tab (Fig. 4.1c) contains the list of databases registered in the module and the flag of the sign of full deleting of the database when making the delete command. In the context menu of the databases' list the user is provided with an opportunity to add, delete and move to the desired database. The "Module" tab contains information about the module of the "DB" subsystem (Fig.4.1d):
Each database contains its own configuration page with the tabs "Data base", "Tables" and "SQL", in case SQL-requests support. Besides the basic operations you can copy the contents of the DB by means of the standard function for the copying the objects in the configurator. The copying operation the DB contents involves the copying of the original database to the destination database, and the contents of the destination database is not cleared before the copy operation. Copying the contents of database is made only when the both databases are enabled, otherwise it will run a simple copy of the object of the database.
Tab "Data base" (Fig.4.1e) contains the main configuration options of the DB as follows:
Tab "Tables" (Fig.4.1f) contains the list of the opened pages. In normal mode of the program operation this tab is empty, because after the completion of working with tables the program closes them. The presence of opened tables tells that the program is now working with tables or tables are opened by the user to examine their contents. In the context menu of list of opened tables you can open the table for study (the command "Add"), close the opened page (the command "Delete") and proceed to examination of the contents of the table.
Tab "SQL" (Fig.4.1g) allow only for data bases which support SQL-requests, and contains field to request enter, button to request send and table to result. To control the request transaction context provided by separate configuration field.
Page of the examination of the contents of the table contains only one tab, "Table". Tab "Table" (Figure 4.1h) contains the field of the name of the table and the table with the contents. Table of contents provides the following functions:
The subsystem is not modular one. To configure the subsystem the root page of the subsystem "Security" is provided, which contains the tab "Users and Groups". Tab "Users and Groups" (Figure 4.2a) contains the list of users and users' groups. Users in the group "Security" and with the rights of the privileged user can add, delete the user or group of users. All other users can go to the page the user or the users' group.
To configure the user it is provided the page containing only the tab "User" (Fig.4.2b). Tab contains the configuration data of the user's profile, which can be changed by the user itself, the user of the "Security" group or the privileged user:
To configure the user's group it is provided the page containing only the tab "Group" (Fig.4.2c). Tab contains the configuration data of the group's profile, which can be changed only by the privileged use:
The subsystem is the modular one and contains the hierarchy of objects shown in Figure 4.3a. To configure the subsystem it is provided the root page of the subsystem "Transports", containing the tabs "Subsystem" and "Modules".
The tab "Subsystem" (Figure 4.3b) contains the configuration table of the external stations for a given OpenSCADA. External stations can be the system, user and both ones that is selected by the appropriate column. System's external stations are available only to the super user and are used by the components of the system purpose, for example, the mechanism of the horizontal redundancy and module DAQ.DAQGate. User's external stations are tied to the user who created them, and thus the list of user's external stations is individual for each user. User's external stations are used by the components of graphical interface, for example, UI.QTCfg, UI.WebCfgD and UI.Vision. In the table of the external stations it is possible to add and delete records about the station, as well as their modification.
Each station contains the following fields:
Tab "Moules" tab (fig. 4.1b) contains the list of modules in subsystem "Transports" and it is identical for all modular subsystems.
Each module of the subsystem "Transports" provides the configuration page with the tabs "Transports" and "Module". The tab "Transports" (Fig.4.3c) contains the list of incoming and outgoing transports registered in the module. The context menu of lists of transports provides the user with the possibility to add, delete and move to the desired transport. On the "Module" tab it is provided the information about the module of subsystem "Transports" (Fig. 4.1d), whose structure is identical for all modules.
Each transport contains its own configuration page with one tab "Transport". This tab contains the basic settings of transport. Incoming transport (fig.4.3d) includes:
Outgoing transport (Fig. 4.3e) contains:
Outgoing transport, in addition, provides the tab for forming the user request via this transport (Fig.4.3f). The tab is provided for setting communication, as well as for debugging the protocols and includes:
The subsystem is modular. To configure the subsystem the root page of the subsystem "Transport Protocols" is provided, it contains tab "Modules". The tab "Modules" (Fig. 4.1b) contains the list of modules in subsystem "Transport Protocols" and is identical for all modular subsystems.
Each module of subsystem "Transport Protocols" provides configuration page with the only one tab "Module". On the tab "Module" there is the information on the module of subsystem "Transport Protocols" (Fig. 4.1d), which structure is identical for all modules.
The subsystem is modular and contains the hierarchy of objects depicted in Fig.4.5a. To configure the subsystem the root page of subsystem "Data acquisition" is provided, which contains the tabs "Redundancy", "Template libraries" and "Modules".
To obtain access to modify the objects of this subsystem the user of the group "DAQ" or the rights of the privileged user are required.
As a redundancy object of the subsystem "Data Acquisition" there used the object of controller for which the redundancy process performs that functions:
Tab "Redundancy" (Fig. 4.5b) presented only if at last one station pointed into the redundancy and contains the configuration of redundancy of data sources of subsystem "Data acquisition" with the following settings:
The tab "Template libraries" (Fig.4.5c) contains the list of libraries of templates for the parameters of this subsystem. In the context menu of the list of template libraries the user can add, delete and move to the desired library. The tab "Modules" (Fig. 4.1b) contains the list of modules in the subsystem "Transports" and is identical for all modular subsystems.
Each template library of subsystem "Data acquisition" provides the configuration page with the tabs "Library" and "Parameter templates". Tab "Library" (fig. 4.5d) contains the basic settings of the library:
Tab "Parameter templates" (Fig.4.5e) contains the list of templates in the library. In the context menu of the list the user can add, delete and move to the desired template.
Each template of the template library provides the configuration page with the tabs "Template" and "IO". The tab "Template" (Figure 4.5f) contains the basic settings of the template:
The tab "IO" (Fig.4.5g) contains the configuration of attributes (IO) of templates and the program of template on the one of languages of the user programming of OpenSCADA, for example, DAQ.JavaLikeCalc.JavaScript. To the table of attributes of template user can, through the context menu, add, insert, delete, move up or down the record of attribute, as well as edit the attribute's fields:
The syntax of the language of the template's program you can see in the documentation of the module, providing an interpreter of the chosen language. For example, a typical user programming language of OpenSCADA DAQ.JavaLikeCalc.
Each module of the subsystem "Data acquisition" provides the configuration page with the tabs "Controllers" and "Module". The tab "Controllers" (Fig.4.5h) contains the list of controllers, registered in the module. In the context menu user can add, delete and move to the desired controller. The tab "Module" provides information about the module of the subsystem "Data acquisition" (Fig. 4.1d), which structure is identical for all modules.
Each controller contains its own configuration page with the tabs "Controller" and "Parameters".
The tab "Controller" (Fig.4.5i) contains the basic settings. The structure of these settings may differ slightly from one module of this subsystem to another, as you can find in the own documentation of modules. As an example, lets examine the settings of the controller in the module of the controller of logic DAQ.LogicLev:
"Parameters" tab (Fig.4.5j) contains a list of parameters in the controller, select the type of parameters that are created by default, as well as information on the total number and the number of enabled parameters. In the context menu user can add, delete and move to the desired parameter.
"Diagnostic" tab (Fig.4.5k) contains diagnostic messages form by the data source. More data sources is external devices with accessing to the data by a network connection or a system bus then there possible different emergency situation on access to the data. Print all its to field "State" of controller object impossible due it display only current access data state. Due the diagnostic you can trace all emergency situation at messages view, which forming by the controller object for specified period of time and by selected messages level. Besides to certain diagnostic information some modules of data sources can provide here debug exchange dumps, on messages level "Debug (0)".
Parameters of the controllers of subsystem "Data acquisition" provides the configuration page with the tabs "Parameters", "Attributes", "Archiving" and "Template config". The tab "Template config" is not standard, but it is present only in the parameters of modules of subsystem "Data acquisition", which implement the mechanisms of working under the template in the context of the data source, which they are served, for logical type. In this review this tab is included for logical completeness of the review of the configuration of templates of parameters of subsystem "Data acquisition" and as the final stage using.
The tab "Parameter" (Fig.4.5l) contains the main settings:
The tab "Attributes" (Fig.4.5m) contains the parametr's attributes and their values in accordance with the configuration of the used template and calculation of its program.
The "Archiving" tab (Fig.4.5n) contains the table with the attributes of a parameter in the columns and the archivers in rows. The user can set the archiving for the desired attribute with the required archiver simply by changing the cell at the intersection.
The "Template config" tab (Figure 4.5o) contains the configuration fields in accordance with the template. In this example it is the group link on the external parameter. This link can be set simply by pointing the way to the parameter if the flag "Only attributes are to be shown" is not set, or to set the addresses of the attributes separately in the case if the flag is set. Sign "(+)", at the end of the address signals about successful linking and presence of the target.
The subsystem is modular and contains the hierarchy of objects depicted in Fig.4.6a. To configure the subsystem the root page of the subsystem "Archives" is provided, it contains tabs: "Redundancy", "Messages archive", "Value archives" and "Modules".
To gain the access to modify the objects of this subsystem the user of the group "Archive" or the privileged user rights are required.
As a redundancy object of the subsystem "Archives" there used the object of messages archivator for which the redundancy process performs that functions:
Redundancy of the value archivators doesn't provided directly but that process does through data sources and the subsystem of "Data acquisition".
Tab "Redundancy" (Fig. 4.6b) presented only if at last one station pointed into the redundancy and contains the configuration of redundancy of messages archvators with the following settings:
The "Messages archive" tab (Fig.4.6c) contains the configuration of messages archive and the request form of messages from the archive.
Configuration of the messages archive is represented by the fields:
The messages request form contains the configuration fields of the request and the table of results. Configuration fields of the request are:
The result table contains rows of messages with the following columns:
Tab "Value archives" (Fig.4.6d) contains the general configuration of value's archiving and the list of archives of values. In the context menu of the list of values the user has the opportunity to add, delete and move to the desired archive. The general configuration of archiving is represented by the fields:
The "Modules" tab (Fig. 4.1b) contains a list of modules in subsystem "Archives" and it is identical for all modular subsystems.
Archive of values of subsystem "Archives" provides the configuration page with the tabs "Archive", "Archivators" and "Values".
Tab "Archive" (Fig.4.6e) contains the basic settings of the archive:
Tab Archivators' (Fig.4.6f) contains the table with the configuration of the processing of the archive by the available archivers. Lines are available archivers, and the columns are the following parameters:
Tab "Values" (Fig.4.6g) contains the values request in the archive and the result as a table of values or image of the trend. Values request contains the fields:
Each module of the "Archives" subsystem provides configuration page with the tabs "Archivators" and "Module". The "Archivators" tab (Fig.4.6h) contains a list of messages and values archivers registered in the module. The context menu of the list provides user with possibility to add, delete and move to the desired controller. The "Module" tab contains information about the module of subsystem "Archives" (Fig. 4.1d), whose structure is identical for all modules.
Messages archivators contains their own configuration page with tabs "Archivator" and "Messages".
The "Archivator" tab (Fig.4.6i) contains the basic settings. The structure of these settings may differ slightly from one module of this subsystem to another as you can find in the own documentation of modules. As an example we shall examine the settings of the messages archiver from the module of the archive on the file system Arch.FSArch Settings:
The "Messages" tab (Fig.4.6j) contains the form of the messages request from the archive of the archiver:
The result table contains messages rows with the following columns:
Values archivers contains their own configuration page with tabs "Archivator" and "Archives".
The "Archivator" tab (Fig.4.6k) contains the basic settings. The structure of these settings may differ slightly from one module of this subsystem to another as you can find in the own documentation of modules. As an example we shall examine the settings of the messages archiver from the module of the archive on the file system Arch.FSArch Settings:
The "Archives" tab (Fig.4.6l) contains a table with information about the archives being processed by the archiver. In the rows the table contains archives, and in the columns the following information:
In the case of the module Arch.FSArch in this tab you can find the form of export the archiver's data.
The subsystem is modular. To configure the subsystem the root page of the subsystem "User Interfaces" is provided, it contains the tab "Modules". The "Modules" tab (Fig. 4.1b) contains a list of modules of subsystem and it is identical for all modular subsystems.
Each module of the subsystem "User Interfaces" provides configuration page with the tabs "User Interface" and "Module". The "User Interface" tab (Fig.4.7a) provides the parameter for monitoring the "Running" status of the module, as well as the configuration sections specialized for the modules of this subsystem. On the "Module" tab there is an information about the module of the subsystem "User Interfaces" (Fig. 4.1d), which structure is identical for all modules.
Each module of the subsystem "Specials" provides configuration page with the tabs "Special" and "Module". The "Special" tab (Fig.4.8a) provides the parameter for monitoring the "Running" status of the module, as well as the configuration sections specialized for the modules of this subsystem. On the "Module" tab there is an information about the module of the subsystem "Specials" (Fig. 4.1d), which structure is identical for all modules.
The subsystem is not modular. To configure the subsystem the subsystem's page "Modules scheduler" is provided, it contains tab "Subsystem". The "Subsystem" tab (Fig.4.9a) contains the basic settings of the subsystem. The structure of the tab "Subsystem":
Configuration file of the OpenSCADA system is provided to store the system and general configuration of OpenSCADA-station. Only in the configuration file and through the command-line options you can specify the part of the key system parameters of the station, so familiarity with the structure of the configuration file is necessary for professionals who make solutions based on OpenSCADA.
The configuration file of the OpenSCADA system can be called somehow, but the oscada.xml name and derived from it are accepted. The configuration file is usually indicated when you start the station by the command-line option "--config=/home/roman/roman/work/OScadaD/etc/oscada_demo.xml". For the convenience of the calling the startup scripts of the station are created with the correct configuration file or used the project manager at start script openscada_start. For example script (openscada_demo) uses for the demo station execution:
#!/bin/sh
openscada --config=/etc/oscada_demo.xml $@
If the configuration file is not specified then the standard configuration file: /etc/oscada.xml is used.
Structure of the configuration file based on the extensible markup language XML. Therefore the strict adherence to the rules of XML syntax is required. An example of the configuration file of the OpenSCADA, with configuration nodes of most of the OpenASCADA components, is given below:
<?xml version="1.0" encoding="UTF-8" ?> <OpenSCADA> <!-- This is the OpenSCADA configuration file. --> <station id="AGLKS"> <!-- Describe internal parameters for station. The station is OpenSCADA program. --> <prm id="StName">AGLKS</prm> <prm id="StName_ru">ΐΓΛΚΡ</prm> <prm id="StName_uk">ΐΓΛΚΡ</prm> <prm id="WorkDB">SQLite.GenDB</prm> <prm id="LogTarget">10</prm> <prm id="Lang2CodeBase">en</prm> <prm id="SaveAtExit">0</prm> <prm id="SavePeriod">0</prm> <node id="sub_BD"> <prm id="SYSStPref">0</prm> <tbl id="DB"> <fld ID="GenDB" TYPE="SQLite" NAME="Generic DB" NAME_ru="Ξρνξβνΰ� ΑΔ" NAME_uk="Ξρνξβνΰ ΑΔ" ADDR="St.db" CODEPAGE="UTF-8"/> </tbl> </node> <node id="sub_Security"> <!-- <tbl id="Security_user"> <fld NAME="root" DESCR="Super user" DESCR_ru="Ρσοεπ οξλόηξβΰςελό" DESCR_uk="Ρσοεπ κξπθρςσβΰχ" PASS="openscada"/> <fld NAME="user" DESCR="System user" DESCR_ru="Ρθρςεμνϋι οξλόηξβΰςελό" DESCR_uk="Ρθρςεμνθι κξπθρςσβΰχ" PASS=""/> </tbl> <tbl id="Security_grp"> <fld NAME="root" DESCR="Super users groups" DESCR_ru="Γπσοοΰ ρσοεποξλόηξβΰςελει" DESCR_uk="Γπσοΰ ρσοεπκξπθρςσβΰχ³β" USERS="root;user"/> </tbl>--> </node> <node id="sub_ModSched"> <prm id="ModAllow">*</prm> <prm id="ModDeny"></prm> <prm id="ChkPer">0</prm> </node> <node id="sub_Transport"> <!-- <tbl id="Transport_in"> <fld ID="WEB_1" MODULE="Sockets" NAME="Generic WEB interface" NAME_ru="Ξρνξβνξι WEB θνςεπτειρ" NAME_uk="Ξρνξβνθι WEB ³νςεπτειρ" DESCRIPT="Generic transport for WEB interface." DESCRIPT_ru="Ξρνξβνξι ςπΰνροξπς δλ� WEB θνςεπτειρΰ." DESCRIPT_uk="Ξρνξβνθι ςπΰνροξπς δλ� WEB ³νςεπτειρσ." ADDR="TCP::10002:0" PROT="HTTP" START="1"/> <fld ID="WEB_2" MODULE="Sockets" NAME="Reserve WEB interface" NAME_ru="Πεηεπβνϋι WEB θνςεπτειρ" NAME_uk="Πεηεπβνθι WEB ³νςεπτειρ" DESCRIPT="Reserve transport for WEB interface." DESCRIPT_ru="Πεηεπβνϋι ςπΰνροξπς δλ� WEB θνςεπτειρΰ." DESCRIPT_uk="Πεηεπβνθι ςπΰνροξπς δλ� WEB ³νςεπτειρσ." ADDR="TCP::10004:0" PROT="HTTP" START="1"/> </tbl> <tbl id="Transport_out"> <fld ID="testModBus" MODULE="Sockets" NAME="Test ModBus" NAME_ru="�ερς ModBus" NAME_uk="�ερς ModBus" DESCRIPT="Data exchange by protocol ModBus test." DESCRIPT_ru="�ερς ξαμενΰ οξ οπξςξκξλσ ModBus." DESCRIPT_uk="�ερς ξαμ³νσ ηΰ οπξςξκξλξμ ModBus." ADDR="TCP:localhost:10502" START="1"/> </tbl>--> </node> <node id="sub_DAQ"> <!-- <tbl id="tmplib"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" DB="tmplib_test2"/> </tbl> <tbl id="tmplib_test2"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" PROGRAM="JavaLikeCalc.JavaScript
cnt=5*i;"/> </tbl> <tbl id="tmplib_test2_io"> <fld TMPL_ID="test2" ID="i" NAME="I" NAME_ru="I" NAME_uk="I" TYPE="4" FLAGS="160" VALUE="" POS="0"/> <fld TMPL_ID="test2" ID="cnt" NAME="Cnt" NAME_ru="Cnt" NAME_uk="Cnt" TYPE="4" FLAGS="32" VALUE="" POS="0"/> </tbl>--> <node id="mod_LogicLev"> <!-- <tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" PERIOD="1000" PRIOR="0"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" MODE="2" PRM="test2.test2"/> </tbl>--> </node> <node id="mod_System"> <!-- <tbl id="DAQ"> <fld ID="DataOS" NAME="Data OS" NAME_ru="Δΰνϋε ΞΡ" NAME_uk="Δΰν³ ΞΡ" DESCR="Data of services and subsystems OS." DESCR_ru="Δΰννϋε ρεπβθρξβ θ οξδρθρςεμ ΞΡ." DESCR_uk="Δΰν³ ρεπβ³ρ³β ςΰ ο³δρθρςεμ ΞΡ." ENABLE="1" START="1" AUTO_FILL="0" PRM_BD="DataOSprm" PERIOD="1000" PRIOR="0"/> </tbl> <tbl id="DataOSprm"> <fld SHIFR="CPU" NAME="CPU load" NAME_ru="Νΰγπσηκΰ CPU" NAME_uk="Νΰβΰνςΰζενν� CPU" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" TYPE="CPU" SUBT="gen"/> <fld SHIFR="MEM" NAME="Memory" NAME_ru="Οΰμ�ςό" NAME_uk="Οΰμ\'�ςό" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" TYPE="MEM"/> </tbl> --> </node> <node id="mod_DiamondBoards"> <!-- <tbl id="DAQ"> <fld ID="Athena" NAME="Athena board" NAME_ru="Ολΰςΰ Athena" NAME_uk="Ολΰςΰ Athena" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="0" BOARD="25" PRM_BD_A="AthenaAnPrm" PRM_BD_D="AthenaDigPrm" ADDR="640" INT="5" DIO_CFG="0" ADMODE="0" ADRANGE="0" ADPOLAR="0" ADGAIN="0" ADCONVRATE="1000"/> </tbl> <tbl id="AthenaAnPrm"> <fld SHIFR="ai0" NAME="AI 0" NAME_ru="AI 0" NAME_uk="AI 0" DESCR="" DESCR_ru="" DESCR_uk="" EN="0" TYPE="0" CNL="0" GAIN="0"/> </tbl> <tbl id="AthenaDigPrm"> <fld SHIFR="di0" NAME="DI 0" NAME_ru="DI 0" NAME_uk="DI 0" DESCR="" DESCR_ru="" DESCR_uk="" EN="0" TYPE="0" PORT="0" CNL="0"/> </tbl> --> </node> <node id="mod_BlockCalc"> <!-- <tbl id="DAQ"> <fld ID="Model" NAME="Model" NAME_ru="Μξδελό" NAME_uk="Μξδελό" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="Model_prm" BLOCK_SH="Model_blcks" PERIOD="1000" PRIOR="0" PER_DB="0" ITER="1"/> </tbl> <tbl id="Model_blcks"> <fld ID="Klap" NAME="Klapan" NAME_ru="Κλΰοΰν" NAME_uk="Κλΰοΰν" DESCR="" DESCR_ru="" DESCR_uk="" FUNC="DAQ.JavaLikeCalc.lib_techApp.klap" EN="1" PROC="1"/> </tbl> <tbl id="Model_blcks_io"> <fld BLK_ID="Klap" ID="l_kl1" TLNK="0" LNK="" VAL="50"/> <fld BLK_ID="Klap" ID="l_kl2" TLNK="0" LNK="" VAL="20"/> </tbl> <tbl id="Model_prm"> <fld SHIFR="l_kl" NAME="Klap lev" NAME_ru="Οξλξζ. κλΰοΰνΰ" NAME_uk="Οξλξζ. κλΰοΰνΰ" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" IO="Klap.l_kl1"/> </tbl> --> </node> <node id="mod_JavaLikeCalc"> <!-- <tbl id="DAQ"> <fld ID="CalcTest" NAME="Calc Test" NAME_ru="�ερς βϋχθρλ." NAME_uk="�ερς ξαχθρλ." DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="CalcTest_prm" FUNC="TemplFunc.d_alarm" SCHEDULE="1" PRIOR="0" ITER="1"/> </tbl> <tbl id="CalcTest_val"> <fld ID="in" VAL="0"/> <fld ID="alrm" VAL=""/> <fld ID="alrm_md" VAL="1"/> <fld ID="alrm_mess" VAL="Error present."/> </tbl> <tbl id="CalcTest_prm"> <fld SHIFR="alrm" NAME="Alarm" NAME_ru="ΐβΰπθ�" NAME_uk="ΐβΰπ³�" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" FLD="alrm"/> </tbl> <tbl id="lib"> <fld ID="TemplFunc" NAME="" NAME_ru="" NAME_uk="" DESCR="" ESCR_ru="" DESCR_uk="" DB="lib_TemplFunc"/> </tbl> <tbl id="lib_TemplFunc"> <fld ID="d_alarm" NAME="Digit alarm" NAME_ru="ΐβΰπθ� οξ δθρκπ." NAME_uk="ΐβΰπ³� ηΰ δθρκπ" DESCR="" FORMULA="alrm=(in==alrm_md)?"1:"+alrm_mess:"0";"/> </tbl> <tbl id="lib_TemplFunc_io"> <fld F_ID="d_alarm" ID="in" NAME="Input" NAME_ru="Βυξδ" NAME_uk="Βυ³δ" TYPE="3" MODE="0" DEF="" HIDE="0" POS="0"/> <fld F_ID="d_alarm" ID="alrm" NAME="Alarm" NAME_ru="ΐβΰπθ�" NAME_uk="ΐβΰπ³�" TYPE="0" MODE="1" DEF="" HIDE="0" POS="1"/> <fld F_ID="d_alarm" ID="alrm_md" NAME="Alarm mode" NAME_ru="Πεζθμ ΰβΰπθθ" NAME_uk="Πεζθμ ΰβΰπ³Ώ" TYPE="3" MODE="0" DEF="" HIDE="0" POS="2"/> <fld F_ID="d_alarm" ID="alrm_mess" NAME="Alarm message" NAME_ru="Ρξξαω. ΰβΰπθθ" NAME_uk="Οξβ³δ. ΰβΰπ³Ώ" TYPE="0" MODE="0" DEF="" HIDE="0" POS="3"/> </tbl>--> </node> <node id="mod_Siemens"> <!-- <tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" PERIOD="1000" PRIOR="0" CIF_DEV="0" ADDR="5" ASINC_WR="0"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" TMPL="S7.ai_man"/> </tbl>--> </node> <node id="mod_SNMP"> <!-- <tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" PERIOD="1000" PRIOR="0" ADDR="localhost" COMM="public" PATTR_LIM="20"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" OID_LS="system"/> </tbl>--> </node> <node id="mod_ModBus"> <!-- <tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" PERIOD="1000" PRIOR="0" TRANSP="Sockets" ADDR="exlar.diya.org" NODE="1"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" ATTR_LS="321:0:tst:Test"/> </tbl>--> </node> <node id="mod_DAQGate"> <!-- <tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" PERIOD="1000" PRIOR="0" SYNCPER="60" STATIONS="loop" CNTRPRM="System.AutoDA"/> </tbl>--> </node> <node id="mod_DCON"> <!--<tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" PERIOD="1" PRIOR="0" ADDR="" REQ_TRY="1"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" MOD_TP="0" MOD_ADDR="1" CRC_CTRL="1"/> </tbl>--> </node> <node id="mod_ICP_DAS"> <!--<tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" PERIOD="1" PRIOR="0" BUS="1" BAUD="115200" LP_PRMS="" REQ_TRY="3"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" MOD_TP="552985" MOD_ADDR="0" MOD_SLOT="1" MOD_PRMS="0"/> </tbl>--> </node> <node id="mod_OPC_UA"> <!--<tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" SCHEDULE="1" PRIOR="0" SYNCPER="60" ADDR="" EndPoint="opc.tcp://localhost:4841" SecPolicy="None" SecMessMode="1" Cert="" PvKey="" AttrsLimit="100"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" ND_LS=""/> </tbl>--> </node> <node id="mod_SoundCard"> <!--<tbl id="DAQ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" ENABLE="1" START="1" PRM_BD="test2prm" CARD="" SMPL_RATE="8000" SMPL_TYPE="1"/> </tbl> <tbl id="test2prm"> <fld SHIFR="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" EN="1" CHANNEL="0"/> </tbl>--> </node> </node> <node id="sub_Archive"> <prm id="MessBufSize">1000</prm> <prm id="MessPeriod">5</prm> <prm id="ValPeriod">1000</prm> <prm id="ValPriority">10</prm> <!-- <tbl id="Archive_mess_proc"> <fld ID="StatErrors" MODUL="FSArch" NAME="Errors" NAME_ru="Ξψθακθ" NAME_uk="Οξμθλκθ" DESCR="Local errors\' archive" DESCR_ru="ΐπυθβ λξκΰλόνϋυ ξωθαξκ" DESCR_uk="ΐπυ³β λξκΰλόνθυ οξμθλξκ" START="1" CATEG="/DemoStation*" LEVEL="4" ADDR="ARCHIVES/MESS/stError/"/> <fld ID="NetRequsts" MODUL="FSArch" NAME="Net requests" NAME_ru="Ρεςεβϋε ηΰοπξρϋ" NAME_uk="Μεπεζεβ³ ηΰοθςθ" DESCR="Requests to server through transport Sockets." DESCR_ru="Ηΰοπξρϋ κ ρεπβεπσ χεπεη ςπΰνροξπς Sockets." DESCR_uk="Ηΰοθςθ δξ ρεπβεπΰ χεπεη ςπΰνροξπς Sockets." START="1" CATEG="/DemoStation/Transport/Sockets*" LEVEL="1" ADDR="ARCHIVES/MESS/Net/"/> </tbl> <tbl id="Archive_val_proc"> <fld ID="1h" MODUL="FSArch" NAME="1hour" NAME_ru="1χΰρ" NAME_uk="1γξδ" DESCR="Averaging for hour" DESCR_ru="Σρπεδνενθε ηΰ χΰρ" DESCR_uk="Σρεπεδνενν� ηΰ γξδθνσ" START="1" ADDR="ARCHIVES/VAL/1h/" V_PER="360" A_PER="60"/> </tbl> <tbl id="Archive_val"> <fld ID="test1" NAME="Test 1" NAME_ru="�ερς 1" NAME_uk="�ερς 1" DESCR="Test 1" DESCR_ru="�ερς 1" DESCR_uk="�ερς 1" START="1" VTYPE="1" BPER="1" BSIZE="200" BHGRD="1" BHRES="0" SrcMode="0" Source="" ArchS=""/> </tbl>--> </node> <node id="sub_Protocol"> </node> <node id="sub_UI"> <node id="mod_QTStarter"> <prm id="StartMod">QTCfg</prm> </node> <node id="mod_WebCfg"> <prm id="SessTimeLife">20</prm> </node> <node id="mod_VCAEngine"> <!-- <tbl id="LIB"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" DB_TBL="wlib_test2" ICO="" USER="root" GRP="UI" PERMIT="436"/> </tbl> <tbl id="wlib_test2"> <fld ID="test2" ICO="" PARENT="/wlb_originals/wdg_Box" PROC="" PROC_ru="" PROC_uk="" PROC_PER="-1" USER="root" GRP="UI" PERMIT="436"/> </tbl> <tbl id="wlib_test2_io"> <fld IDW="test2" ID="name" IO_VAL="Test 2" IO_VAL_ru="�ερς 2" IO_VAL_uk="�ερς 2" SELF_FLG="" CFG_TMPL="" CFG_TMPL_ru="" CFG_TMPL_uk="" CFG_VAL=""/> <fld IDW="test2" ID="dscr" IO_VAL="Test module 2" IO_VAL_ru="�ερς μξδσλ� 2" IO_VAL_uk="�ερς μξδσλ� 2" SELF_FLG="" CFG_TMPL="" CFG_TMPL_ru="" CFG_TMPL_uk="" CFG_VAL=""/> </tbl> <tbl id="PRJ"> <fld ID="test2" NAME="Test 2" NAME_ru="�ερς 2" NAME_uk="�ερς 2" DESCR="" DESCR_ru="" DESCR_uk="" DB_TBL="prj_test2" ICO="" USER="root" GRP="UI" PERMIT="436"/> </tbl> <tbl id="prj_test2"> <fld OWNER="/test2" ID="pg1" ICO="" PARENT="/wlb_originals/wdg_Box" PROC="" PROC_ru="" PROC_uk="" PROC_PER="-1" USER="root" GRP="UI" PERMIT="436" FLGS="1"/> <fld OWNER="/test2/pg1" ID="pg2" ICO="" PARENT="/wlb_originals/wdg_Box" PROC="" PROC_ru="" PROC_uk="" PROC_PER="-1" USER="root" GRP="UI" PERMIT="436" FLGS="0"/> </tbl> <tbl id="prj_test2_incl"> <fld IDW="/prj_test2/pg_pg1" ID="wdg1" PARENT="/wlb_originals/wdg_Box"/> </tbl>--> </node> </node> <node id="sub_Special"> <node id="mod_SystemTests"> <prm id="Param" on="0" per="5" name="LogicLev.experiment.F3"/> <prm id="XML" on="0" per="10" file="/etc/oscada.xml"/> <prm id="Mess" on="0" per="10" categ="" arhtor="DBArch.test3" depth="10"/> <prm id="SOAttach" on="0" per="20" name="../../lib/openscada/daq_LogicLev.so" mode="0" full="1"/> <prm id="Val" on="0" per="1" name="LogicLev.experiment.F3.var" arch_len="5" arch_per="1000000"/> <prm id="Val" on="0" per="1" name="System.AutoDA.CPULoad.load" arch_len="10" arch_per="1000000"/> <prm id="DB" on="0" per="10" type="MySQL" addr="server.diya.org;roman;123456;oscadaTest" table="test" size="1000"/> <prm id="DB" on="0" per="10" type="DBF" addr="./DATA/DBF" table="test.dbf" size="1000"/> <prm id="DB" on="0" per="10" type="SQLite" addr="./DATA/test.db" table="test" size="1000"/> <prm id="DB" on="0" per="10" type="FireBird" addr="server.diya.org:/var/tmp/test.fdb;roman;123456" table="test" size="1000"/> <prm id="TrOut" on="0" per="1" addr="TCP:127.0.0.1:10001" type="Sockets" req="time"/> <prm id="TrOut" on="0" per="1" addr="UDP:127.0.0.1:10001" type="Sockets" req="time"/> <prm id="TrOut" on="0" per="1" addr="UNIX:./oscada" type="Sockets" req="time"/> <prm id="TrOut" on="0" per="1" addr="UDP:127.0.0.1:daytime" type="Sockets" req="time"/> <prm id="SysContrLang" on="0" per="10" path="/Archive/FSArch/mess_StatErrors/%2fprm%2fst"/> <prm id="ValBuf" on="0" per="5"/> <prm id="Archive" on="0" per="30" arch="test1" period="1000000"/> <prm id="Base64Code" on="0" per="10"/> </node> </node> </station> </OpenSCADA>
Lets examine in details the structure of the configuration file. A configuration file can contain a configuration of several stations in the sections <station id="AGLKS"/>. To attribute set the identifier of the station. Using one or another section of the station at startup is specified by the command-line option --station=AGLKS. Section of the station directly contains parameters of the station and subsystems' sections. Configuration options of the section are written in the form <prm id="StName">AGLKS</prm>. Where in the attribute <id> the ID of the attribute is specified, and in the tag's body the value of parameter "AGLKS" is specified. The list of available options and their description for the station and all other sections can be obtained from the console by calling OpenSCADA with parameter --help.
Sections of subsystem (<node id="sub_DAQ" />) contains parameters of subsystem, sections of modules and sections of tables of reflections of the data of databases in the configuration file. Sections of modules (<node id="mod_DiamondBoards" />) contain the individual parameters of modules and sections of tables of reflection of the data of databases in the configuration file.
Sections of the tables of reflection of the data of databases are provided for placement in the configuration file records of DB tables for the OpenSCADA components. Lets examine the table of incoming transports "Transport_in" of subsystem transports (<node id="sub_Transport">) from the example of configuration file above. The table contains two records with fields: ID, MODULE, NAME, DESCRIPT, ADDR, PROT, START. After booting with this section and in general without the DB in the subsystem "Transports" of the "Sockets" module you'll see two input transports. Formats of the table's structures of the main components are included in the demo configuration files. For the details of the database's structure you should read the relevant documentation of modules or simple save the object into the configuration file.
The result of the command: # ./openscada_AGLKS --help
| 2016-09-29 13:10:42 | (131 Kb) | The "Messages archive" tab of the subsystem "Archives". | ||
| 2014-07-13 09:50:35 | (62 Kb) | The "Archivators" tab of the module of subsystem "Archives". | ||
| 2014-07-13 11:36:42 | (93 Kb) | The main tab of the messages archiver configuration of subsystem "Archives". | ||
| 2016-09-29 13:12:53 | (155 Kb) | Tab of the messages request "Messages" of the messages archiver of subsystem "Archives". | ||
| 2013-01-28 21:11:14 | (86 Kb) | The "Archives" tab of the values archiver of subsystem "Archives". | ||
| 2014-07-13 10:10:14 | (107 Kb) | The main tab of the values archiver configuration of subsystem "Archives". | ||
| 2016-06-17 12:44:21 | (80 Kb) | The "Redundancy" tab of subsystem "Archives". | ||
| 2010-01-23 15:42:49 | (24 Kb) | The hierarchical structure of subsystem Archives | ||
| 2016-05-23 16:09:01 | (76 Kb) | The "Value archives" tab of the subsystem "Archives". | ||
| 2016-05-23 16:10:47 | (138 Kb) | The main configuration tab of the values' archive of subsystem "Archives". | ||
| 2013-01-28 21:01:23 | (72 Kb) | The "Archivators" tab of the values archive of subsystem "Archives". | ||
| 2013-01-28 21:02:42 | (109 Kb) | The "Values" tab of the values archive of subsystem "Archives". | ||
| 2013-01-26 20:22:51 | (135 Kb) | "Diagnostic" tab of configuration page of the controller of subsystem "Data acquisition". | ||
| 2014-07-13 09:35:47 | (66 Kb) | The tab "Controllers" of the module of the subsystem "Data acquisition". | ||
| 2013-01-28 20:46:15 | (78 Kb) | The main configuration tab of the controller of subsystem "Data acquisition". | ||
| 2013-01-28 20:55:56 | (58 Kb) | The "Archiving" tab of the parameter of the controller of subsystem "Data acquisition". | ||
| 2013-01-28 20:54:40 | (55 Kb) | The "Attributes" tab of the parameter of the controller of subsystem "Data acquisition". | ||
| 2013-01-28 20:47:47 | (62 Kb) | "Parameters" tab of the configuration page of the controller of subsystem "Data acquisition". | ||
| 2013-01-28 20:53:34 | (55 Kb) | The main configuration tab of the parameter of the controller of subsystem "Data acquisition". | ||
| 2013-01-28 20:57:24 | (65 Kb) | The "Template config" tab of the parameter of the controller of subsystem "Data acquisition". | ||
| 2016-07-26 10:44:54 | (104 Kb) | Tab "Redundancy" tab of subsystem "Data acquisition". | ||
| 2010-01-23 14:34:00 | (41 Kb) | The hierarchical structure of subsystem Data acquisition. | ||
| 2014-07-13 09:34:06 | (56 Kb) | The tab "Template libraries" of the subsystem "Data acquisition". | ||
| 2013-09-06 11:51:59 | (67 Kb) | The main tab of configuration of template library of subsystem "Data acquisition". | ||
| 2013-09-06 11:53:58 | (61 Kb) | The tab of the list of templates in the template library of subsystem "Data acquisition". | ||
| 2016-10-17 12:17:44 | (139 Kb) | The configuration tab of the attributes and template's program of subsystem "Data acquisition". | ||
| 2013-09-06 11:56:02 | (77 Kb) | The main configuration tab of the parameters template of subsystem "Data acquisition". | ||
| 2013-01-28 20:08:05 | (80 Kb) | Tab "Data base" of the DB of module of subsystem "DB". | ||
| 2014-07-13 08:37:10 | (61 Kb) | "DB" tab of the module of "DB" subsystem. | ||
| 2013-01-28 20:12:35 | (106 Kb) | Tab "SQL" of the DB of module of subsystem "DB". | ||
| 2013-01-28 20:09:59 | (50 Kb) | Tab "Tables" of the DB of module of subsystem "DB". | ||
| 2013-01-28 20:14:11 | (99 Kb) | Tab "Table" of the DB table of the module of the subsystem "DB". | ||
| 2014-07-13 08:34:13 | (58 Kb) | Tab "Modules" tab of the root page of "DB" subsystem. | ||
| 2014-07-13 08:41:03 | (72 Kb) | "Module" tab of the module of the "DB" subsystem. | ||
| 2010-01-23 13:13:25 | (37 Kb) | The hierarchical structure of DB subsystem. | ||
| 2014-07-13 10:15:13 | (142 Kb) | The main configuration tab of subsystem "Modules scheduler". | ||
| 2014-07-13 09:20:14 | (57 Kb) | Tab "Users and Groups" of the root page of the subsystem "Security". | ||
| 2016-10-05 11:27:00 | (60 Kb) | The tab "Group" of the user's group page of "Security" subsystem. | ||
| 2016-10-05 11:35:20 | (77 Kb) | The tab "User" of the user's page of "Security" subsystem. | ||
| 2014-07-13 10:13:40 | (66 Kb) | The "Special" tab of the module of subsystems "Specials". | ||
| 2014-07-13 09:23:41 | (64 Kb) | The tab "Transports" of the module of subsystem "Transports". | ||
| 2014-07-13 09:26:35 | (85 Kb) | Tab "Transport" of the page of incoming transport of module of subsystem "Transports". | ||
| 2016-07-26 10:36:59 | (89 Kb) | Tab "Transport" of the page of outgoing transport of module of subsystem "Transports". | ||
| 2016-07-26 10:39:52 | (99 Kb) | The tab "Request" of the page of outgoing transport of module of subsystem "Transports". | ||
| 2010-01-23 14:25:39 | (20 Kb) | The hierarchical structure of subsystems Transports. | ||
| 2016-05-29 21:41:59 | (77 Kb) | Tab "Subsystem" of the root page of subsystem "Transports". | ||
| 2014-07-13 10:11:34 | (70 Kb) | The "User Interface" tab of the module of subsystem "User Interfaces". | ||
| 2017-05-08 11:33:47 | (98 Kb) | The "Debug" tab of the main page of the configuration of the station. | ||
| 2016-04-29 11:26:29 | (93 Kb) | The "Redundancy" tab of the main page of the configuration of the station. | ||
| 2016-07-25 16:58:17 | (156 Kb) | The "Station" tab of the main page of the configuration of the station. | ||
| 2015-06-01 15:09:15 | (76 Kb) | The "Subsystems" tab of the main page of the configuration of the station. | ||
| 2015-06-01 15:17:17 | (196 Kb) | The "Tasks" tab of the main page of the configuration of the station. | ||
| 2015-06-01 16:13:30 | (158 Kb) | The "Translations" tab of the main page of the configuration of the station. |
