Introduction

The module provides the OpenSCADA system with the support of various equipment of "ICP DAS" company (http://www.icpdas.com) through the API library libi8k.a from the company, for modules I-87xxx and I-8xxx, and direct ioctl calls to Linux kernel modules for boards on bus ISA.


Most of the equipment of the "ICP DAS" company is working under the DCON protocol, but some new equipment such as I-8xxx Series operates on a parallel bus, while another part is set into the parallel bus slots (I-87xxx) which are available under the serial interface and DCON protocol, they are not addressed directly and require call of the specialized command of the slot selection. Access to equipment that uses direct requests under the DCON protocol, can be implemented by the module DAQ.DCON. Support for the rest of the equipment is not added to the module DAQ.DCON, but it was implemented in this module due to the availability of API library of the "ICP DAS" company only for the x86_32 and ARM(OABI, HardFloatFPA) platform, which brings restrictions on access to the equipment of the ICP DAS company and other equipment under the DCON protocol on the other hardware platforms.


The reason for creating this module was the works with the controller LP-8781 of "LinPAC" series of "ICP DAS" company with the purpose to implement runtime PLC based on the OpenSCADA system.


API library of the "ICP DAS" company for platform x86_32 -> libi8k.a and ARM(OABI, HardFloatFPA) -> libi8k_arm.a is available with source code of the module and does not require separate installation.

1. Data controller

To add the "ICP DAS" data source the controller is created and configured in the OpenSCADA system. Example of the configuration tab of the controller of this type is shown in Figure 1.


Configuration tab of the controller. (96 Êá)
Fig.1. Configuration tab of the controller.

From this tab you can set:

2. Parameters

The module provides only one type of parameters — "Standard" and three groups of modules/boards, accessable dependent from selected bus:


Configuration tab of the parameter. (70 Êá)
Fig.2. Configuration tab of the parameter.

The configuration tab of parameter (fig.2) generally equal for all modules/boards groups and contain:


In accordance with the parameter settings the poll and the creation of attributes is made (Fig. 3).


Tab of the attributes of the parameter. (76 Êá)
Fig.3. Tab of the attributes of the parameter.

2.1 The modules I-8xxx series

The modules I-8xxx series inserting on parallel bus slot of controller, for example LinPAC series. Into table 1 listed properties modules "ICP DAS" of I-8xxx series, which implemented into OpenSCADA.


Table 1 Properties of modules I-8xxx series

Module AI AO DI DO Notes
I-8014 i8014W_ReadAI() or i8014W_ReadFIFO() for mode FIFO(Magic) Tested!
I-8017 I8017_GetCurAdChannel_Float_Cal() Tested!
I-8024 I8024_VoltageOut
I-8037 DO_16, DO_16_RB
I-8040 DI_32
I-8041 DO_32, DO_32_RB
I-8042 DI_16 DO_16, DO_16_RB Tested!
I-8046 DI_16
I-8048 DI_8
I-8050 DIO_DI_16 DIO_DO_16
I-8051 DI_16
I-8052 DI_8
I-8053 DI_16
I-8054 DI_8 DO_8, DO_8_RB
I-8055 DI_8 DO_8, DO_8_RB
I-8056 DO_16, DO_16_RB
I-8057 DO_16, DO_16_RB
I-8058 DI_8
I-8060 DO_8 (6), DO_8_RB
I-8063 DI_8 (4) DO_8 (4), DO_8_RB
I-8064 DO_8, DO_8_RB
I-8065 DO_8, DO_8_RB
I-8066 DO_8, DO_8_RB
I-8068 DO_8, DO_8_RB
I-8069 DO_8, DO_8_RB
I-8077 DIO_DI_16 DIO_DO_16

2.1.1 Controllers LP-8xxx series configuration

For common properties the controllers series LP-8xxx configuration allowed accordingly "LinPAC" tab on controller's page (Fig.4), and also by parameter "LP-8xxx" (Fig.5). Into parameter "LP-8xxx" you can get information about controller's serial number, SDK version, DIP and Rotary switch value. Into tab "LinPAC" you can set value for controller's watchdog timer. The watchdog timer is disabled by set it to zero value. Watchdog timer's value updated into controller's task and with it period, then the acquisition task hang consequently follow controller's restart! The watchdog value must be greater to the system full loading time, up to OpenSCADA loading, wherein OpenSCADA must be loaded after time sync start.


"LinPAC" tab for controllers LP-8xxx series configuration (58 Êá)
Fig.4. "LinPAC" tab for controllers LP-8xxx series configuration

Parameter "LP-8xxx" attributes. (64 Êá)
Fig.5. Parameter "LP-8xxx" attributes.

2.1.2 Module I-8014 and I-8017

Fast analog input modules that runs on a parallel bus.


The module I-8014 formal provides speed access to data on one channel at 250 kHz by FIFO, however, because of the pledged hardware-program limitations it does not allow to reach speed over 100 kHz per channel when scanning into real-time, by low reading speed from FIFO. In that time the data reading causes the main CPU high load, that is 9.5 microseconds per sample.


The module I-8017 formal provides speed access to data on one channel at 130 kHz, however, because of the pledged hardware-program limitations it does not allow to reach speed over 33 kHz per channel when scanning multiple channels into real-time (by switching). Data expectation is in the blind cycle, which leads to great losses of the CPU at high frequencies of the acquisition.


The modules provides sixteen analog input attributes ai{x} and eight signs of violation of the upper ha{x} and the lower la{x} boundaries, for I-8017. Also "Configuration" tab is available with advanced configuration (Fig.6):


Tab "Configuration" of module I-8017 (82 Êá)
Fig.6. Tab "Configuration" of modules I-8014 and I-8017

2.1.3 Digital input and output values inversion

For digital input and output modules, into tab "Configuration" (Fig.7), proposed selectable channel inversion function, that is too comfortably for next work with the channel.


Tab "Configuration" of module digital input and output (63 Êá)
Fig.7. Tab "Configuration" of module digital input and output

2.2 Module I-87xxx series

The modules I-87xxx series inserting on serial bus slot of controller, for example LinPAC series. Into table 2 listed properties modules "ICP DAS" of I-87xxx series, which implemented into OpenSCADA.


Table 2 Properties of modules I-87xxx series

Module AI AO DI DO Counters Notes
I-87005 #AA (8); TP: $AA7CiRrr ($AA8Ci) @AADODD (8), @AADI
I-87013 #AA (4); TP: $AA7CiRrr ($AA8Ci)
I-87015 #AA (7); TP: $AA7CiRrr ($AA8Ci)
I-87016 #AA (2); TP: $AA7CiRrr ($AA8Ci)
I-87017 #AA (8); TP: $AA7CiRrr ($AA8Ci)
I-87017DW #AA (16); TP: $AA7CiRrr ($AA8Ci)
I-87017ZW #AA (20); TP: $AA7CiRrr ($AA8Ci) Tested!
I-87018 $AA3; #AA (8); TP: $AA7CiRrr ($AA8Ci)
I-87018ZW $AA3; #AA (10); TP: $AA7CiRrr ($AA8Ci)
I-87019RW $AA3; #AA (8); TP: $AA7CiRrr ($AA8Ci) Tested!
I-87019ZW $AA3; #AA (10); TP: $AA7CiRrr ($AA8Ci)
I-87022 #AAN(Data) (2), $AA8N; W: ~AA0-5
I-87024 #AAN(Data) (4), $AA8N; W: ~AA0-5 Tested!
I-87026 #AAN(Data) (2), $AA8N; W: ~AA0-5
I-87026PW #AA (6); TP: $AA7CiRrr ($AA8Ci) #AAN(Data) (2), $AA8N; W: ~AA0-5 @AADI (2) @AADODD (2), @AADI
I-87028 #AAN(Data) (8), $AA8N; W: ~AA0-5
I-87037 @AA(Data) (16), @AA; W: ~AA0-5
I-87040 @AA (32) #AAN (32) Tested!
I-87041 @AA(Data) (32), @AA; W: ~AA0-5 Tested!
I-87042 @AA (16) @AA(Data) (16), @AA; W: ~AA0-5
I-87046 @AA (16) #AAN (16)
I-87051 @AA (16) #AAN (16)
I-87052 @AA (8) #AAN (8)
I-87053 @AA (16) #AAN (16)
I-87054 @AA (8) @AA(Data) (8), @AA; W: ~AA0-5 #AAN (8)
I-87055 @AA (8) @AA(Data) (8), @AA; W: ~AA0-5 #AAN (8)
I-87057 @AA(Data) (16), @AA; W: ~AA0-5
I-87058 @AA (8) #AAN (8)
I-87059 @AA (8) #AAN (8)
I-87061 @AA(Data) (16), @AA; W: ~AA0-5
I-87063 @AA (16) @AA(Data) (16), @AA; W: ~AA0-5 #AAN (16)
I-87064 @AA(Data) (8), @AA; W: ~AA0-5
I-87065 @AA(Data) (8), @AA; W: ~AA0-5
I-87066 @AA(Data) (8), @AA; W: ~AA0-5
I-87068 @AA(Data) (8), @AA; W: ~AA0-5
I-87069 @AA(Data) (8), @AA; W: ~AA0-5

2.2.1 Abstract module I-87xxx series

Besides support for modules into table 2 this modules group provide abstract module "I-87xxx" implementation, on select which to user will possible set quantity and types for generic connected module's signals: AI, AO, DI, DO and Counters. The function also selectable accessed for modules which containing signals AO and Counters and allows to limit processed channels quantity, for traffic decrease on the serial interface.


This abstract module "I-87xxx" you can use for modules "ICP DAS" I-7xxx series on "pure" serial bus.


Fields for signals quantity and types set provided into main tab of the parameter object configuration page (Fig.8).


Main tab of parameter of abstract module "I-87xxx" (99 Êá)
Fig.8. Main tab of parameter of abstract module "I-87xxx"

2.2.2 Channel type select for AI

For analog input modules possible to select mode/gain, which doing from list (Fig.9), if it specified for the module, or direct by mode's code set. The modes saved and stored into the module.


Tab "Configuration" of analog inputs module (89 Êá)
Fig.9. Tab "Configuration" of analog inputs module

2.2.3 Host watchdog and default values for power on and by watchdog event

Modules with analog or digital outputs typical provide host watchdog function. And its sets safe outputs values on host activity miss for specified time. Also the modules allow specify outputs values for power on.


On Figure 10 presented tab for module with analog outputs and functions:


Tab "Configuration" of analog outputs module (79 Êá)
Fig.10. Tab "Configuration" of analog outputs module

2.3 Boards on bus ISA

The type boards installed on bus ISA of personal computer. For work with this boards you need build and start drivers-modules for Linux kernel. Into table 3 listed properties boards "ICP DAS" on bus ISA, which implemented into OpenSCADA.


 (2 Kb) Counters function is not currently implemented into OpenSCADA.

Table 3 Properties of boards on bus ISA

Module AI AO DI DO DIO Counters Notes
A-626 IXISA_AO{0...5} IXISA_DI_{A...B} IXISA_DO_{A...B}
A-628 IXISA_AO{0...7} IXISA_DIO_{A...B} IXISA_DIO_{A...B}
A-8111 IXISA_AI (8,12)
IXISA_ADGCR
IXISA_ADMXCR
IXISA_ADMCR
IXISA_ADSTCR
IXISA_AO{0...1} IXISA_DI{L,H} IXISA_DO{L,H} IXISA_8254C{0...2}
IXISA_8254CR
A-812 IXISA_AI (16,12)
IXISA_ADGCR
IXISA_ADMXCR
IXISA_ADMCR
IXISA_ADSTCR
IXISA_AO{0...1} IXISA_DI{L,H} IXISA_DO{L,H} IXISA_8254C{0...2}
IXISA_8254CR
A-821 IXISA_AI (16,12)
IXISA_ADGCR
IXISA_ADMXCR
IXISA_ADMCR
IXISA_ADSTCR
IXISA_AO IXISA_DI{L,H} IXISA_DO{L,H} IXISA_8254C{0...2}
IXISA_8254CR
A-822 IXISA_AI (16,12)
IXISA_ADGCR
IXISA_ADMXCR
IXISA_ADMCR
IXISA_ADSTCR
IXISA_AO{0...1} IXISA_DI{L,H} IXISA_DO{L,H} IXISA_8254C{0...2}
IXISA_8254CR
A-823 IXISA_AI (16,12)
IXISA_ADGCR
IXISA_ADMXCR
IXISA_ADMCR
IXISA_ADSTCR
IXISA_AO{0...1} IXISA_DI{L,H} IXISA_DO{L,H} IXISA_8254C{0...2}
IXISA_8254CR
A-826 IXISA_AI (16,16)
IXISA_ADGCR
IXISA_ADMXCR
IXISA_ADMCR
IXISA_ADSTCR
IXISA_AO{0...1} IXISA_DI{L,H} IXISA_DO{L,H} IXISA_8254C{0...2}
IXISA_8254CR
DIO-144 IXISA_CN{0...5}P{A...C}
IXISA_CN{0...5}CR
Tested!
DIO-24 IXISA_P{A...C}
IXISA_CR
DIO-48 IXISA_CN{1...2}P{A...C} IXISA_CN{1...2}CR
IXISA_8254C{0...2}
IXISA_8254CR
DIO-64 IXISA_DIO_{A...D} IXISA_DIO_{A...D} IXISA_8254C{0...5}
IXISA_8254CR
IXISA_8254CR1
DIO-96 IXISA_CN{0...3}P{A...C}
IXISA_CN{0...3}CR
ISO-730 IXISA_IDIO_{A...B}
IXISA_DIO_{A...B}
IXISA_IDIO_{A...B}
IXISA_DIO_{A...B}
ISO-813 IXISA_AI (32)
IXISA_ADGCR
IXISA_ADMXCR
IXISA_ADSTCR
ISO-AD32 ==FIFO==
ISO-C64 IXISA_DO_{A...H}
ISO-DA16 ?
ISO-P32C32 IXISA_DIO_{A...D} IXISA_DIO_{A...D}
ISO-P64 IXISA_DI_{A...H}
P16R16DIO IXISA_DI_{A...B} IXISA_DO_{A...B}
P8R8DIO IXISA_DI (8) IXISA_DO (8)
TMC-10 IXISA_DI_{A...B} IXISA_DO_A IXISA_8254C{0...2}
IXISA_8254CR
IXISA_8254CS

Links

Special modules for Linux kernel 2.6.29-rt-up for controllers LP-8x81: lp8x81_2629rt_up.tgz
Special modules for Linux kernel 2.6.29-rt1-up for controllers LP-8x81: lp8x81_2629rt1_up.tgz
The driver from VIA for controllers LP-8x81 network: rhinefet20070212111037.tgz
The patch for build network driver "rhinefet" for Linux 2.6.29: rhinefet_build_to_2.6.29.patch
The patch for build network driver "rhinefet" for Linux 2.6.29-rt1: rhinefet_build_to_2.6.29rt1.patch.gz


Drivers set for Linux for ISA boards: ixisa0.17.0.1.tgz


Referring pages: HomePageEn/Doc
HomePageEn/Function
HomePageEn/Using/LP8x81
HomePageEn/Using/PLC/firmware


 
Files[Hide files/form]
2014-02-21 12:49:41    (58 Kb)  cfg_lp8xxx.png "LinPAC" tab for controllers LP-8xxx series configuration
2011-04-05 12:51:08    (25 Kb)  daq_icp_das_en.odt The document in format OpenDocument
2014-02-21 12:45:50    (96 Kb)  icp_cntr.png Configuration tab of the controller.
2014-02-21 12:47:01    (70 Kb)  icp_prm.png Configuration tab of the parameter.
2014-02-21 12:48:22    (76 Kb)  icp_prm_atr.png Tab of the attributes of the parameter.
2014-02-21 12:51:11    (64 Kb)  icp_prm_lp8xxx.png Parameter "LP-8xxx" attributes.
2014-02-21 12:52:24    (82 Kb)  mod_cfg_8017.png Tab "Configuration" of module I-8017
2014-02-21 12:58:10    (89 Kb)  mod_cfg_ai.png Tab "Configuration" of analog inputs module
2014-02-21 12:59:33    (79 Kb)  mod_cfg_ao.png Tab "Configuration" of analog outputs module
2014-02-21 12:53:51    (63 Kb)  mod_cfg_dio.png Tab "Configuration" of module digital input and output
2014-02-21 12:55:19    (99 Kb)  mod_prm_i87xxx.png Main tab of parameter of abstract module "I-87xxx"
2014-02-21 12:56:50    (99 Kb)  mod_prm_i87xxx.png Main tab of parameter of abstract module "I-87xxx"
There is no comment on this page. [Display comments/form]